Subject: Re: [Equest-users] Unmet Hours
Gerry,
The summary report in eQUEST illustrate noncoincidental unmet load hours
while the BEPS shows coincidental unmet load hours. I did not open your
file, but I'm guessing you have core and perimeter zones with unmet load
hours at different times due to their load profiles. When I have that many
unmet cooling load hours on my BEPS reports I usually do one of the
following:
1) Look for a rogue zone causing issue
2) Look at the 'big' picture (i.e. did I specify a schedule or have
another input that conflicts in the model and is preventing proper cooling).
3) After exhausting all other resources, I start manually increasing my
airflows in individual zones to decrease the unmet load hours.
I hope this helps.
Thanks,
David W. Griffin II
Energy Analyst
ETC Group, LLC
801-278-1927 x 128
Cell 480-736-2945
dgriffin at etcgrp.com
www.etcgrp.com
Copy of ETC_LogoOnly2_rgb_sm.png
Energy Engineering for a Sustainable Future
1997 South 1100 East, Salt Lake City, UT 84106-4471
----------------------------------------------------------------------------
---------------------------------------
CONFIDENTIALITY NOTICE This e-mail transmission, and any documents, files or
previous e-mail messages attached to it may contain confidential information
that is legally privileged. If you are not the intended recipient or the
person responsible for delivering it to the intended recipient, you are
hereby notified that any disclosure, copying, distribution or use of any of
the information contained in or attached to this transmission is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone at (801) 278-1927 and destroy the
original transmission and its attachments without reading them. Thank you.
From: Gerard Hazel [mailto:ghazel at meengineers.com]
Sent: Thursday, January 30, 2014 4:01 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Unmet Hours
Hi All,
I have used the summary report to identify systems/zones with unmet cooling
hours and addressed them to the point that the report now shows no one zone
with more than 233. However, when I check the BEPS it shows 2174. I have not
come across this before. I am hoping someone can shed some light on my next
move.
Thanks,
Gerry Hazel
Gerard Hazel
M&E Engineers, Inc.
908-526-5700 x14
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4259 / Virus Database: 3684/7050 - Release Date: 01/31/14
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140201/c79d3ba4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1559 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140201/c79d3ba4/attachment.jpeg>
More information about the Equest-users
mailing list