There is an option for “Load-Reset” which will vary the chilled water supply temperature based on load.  You will not need a schedule for the control option.
To verify if you set point is working I suggest you create hourly variable outputs of leaving chilled water temperature, entering condenser water (if applicable), chiller assigned loads, and chiller electricity.  You can calculate the kw/ton for each condition and see where you are not getting your expected results.  If you are trying to model a specific chiller then you will have to generate custom curves to get the correct efficiency at each supply temperature.
John Grando BEMP | CEM | LEED AP BD+C | Associate
Phone: 212-615-3705 | Fax: 212-615-3700
jgrando at cosentini.com
Cosentini Associates - A Tetra Tech Company
Two Pennsylvania Plaza - Third Floor - New York, NY 10121
www.cosentini.com<http://www.cosentini.com/>
NOTICE OF CONFIDENTIALITY
This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof.  In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law.  If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission.  Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege.  If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140115/ae2c1df6/attachment.htm>
    
    
More information about the Equest-users
mailing list