>I need to know how to assign to a new floors (which have been created by de
detailed mode) de "Zones" because it seems to not be there (it appears a
"shadow" with little dots).
Its a pretty manual process to create zones in floors created by detailed
data edit.  If I were you, if possible, Id go back to the wizard mode to
create those floors and zones.  If youve already done too much work in
detailed data edit and dont want to go back to the wizard (and then have to
repeat the work youve done in DD edit), I suggest creating those floors in
a new project (or new projects) via the wizard and then importing them into
your current project?  This is an especially good process if youre adding
floors above current floors.  The imported zones will come in directly below
the current zones in the detail list.  You can position the new floors
wherever youd like.  Directions for doing the import are in the manual.
 
 
-It´s a 15-floors building: if I layered out my 15-floor one obove the next,
why in the different floors appears to be extrerior roof?
It is likely because the floor above isnt completely zoned.  If you cant
go back to the wizard, youll have to add interior ceilings and delete the
roofs where needed.  Again, if you can, Id just go back to the wizard and
fix the zones. The roofs should propagate appropriately once the zones are
fixed.
 
 
 