Hi Omar,
For estimating proposed buildings cooling/heating  efficiencies you can 
follow any of two method's mentioned below-
1. You can use default heating cooling efficiencies as per USGBC DES 
modelling document.
2. You have to calculate manually heating and cooling efficiencies of 
whole plant( Including Cooling tower , pumps, chillers etc.) at part 
load i.e DES system capacity.
I would suggest that modelling of whole system is not required when DES 
option is availed.
Thanks & Regards
Rajendra Choudhary
Sr.Energy Analyst
  
e: rajendra at kalpakrit.com
On 1/6/2014 10:12 PM, Scott Parker wrote:
>
> Omar,
>
> For the "modeling" option you will need to model the plant with the 
> assumed full load (which includes more than just the one building).  
> In a separate energy mode: Run an energy model with load from all 
> buildings on it, and then use the average efficiency (e.g. kW/ton, 
> COP, etc) in the building model as a constant efficiency for the whole 
> year.
>
> For example, from the plant model you may come up with a COP = 5.1 as 
> an _annual average_.  Then the building model would use COP = 5.1 as a 
> _constant value_.
>
> I'll leave it up to you to determine the best way to model the full 
> load on the DES plant, but this could be estimated with a relatively 
> simple model.  The modeling software Trace has a specific feature for 
> this, but you can manually do this in eQuest with a little work.
>
> Regards,
>
> Scott
>
> *From:* equest-users-bounces at lists.onebuilding.org 
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Omar Katanani
> *Sent:* Monday, January 06, 2014 11:30 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Modeling District Energy Systems for LEED
>
> Dear Sirs,
>
> I am modeling a school building for LEED which has a Campus Energy 
> System (water cooled chiller and diesel boiler). The DES was installed 
> almost 8 months ago for the first phase of the project.
>
> Now, I am modeling for the project's second phase, and additional 
> chillers / boilers will be added to the DES in order to be able to 
> serve both phases in addition to any potential building on campus in 
> the future.
>
> 1)Looking at the USGBC's guidance for DES (Appendix C): in order to 
> determine the proposed building heating / cooling efficiency, I guess 
> I have to go with the "Modeling" option because the DES will be 
> expanded as part of my project (so it's not existing).
>
> For this option, do I have to create a separate model of the district 
> plant, or shall I add this district plant to my project's model? 
> Appendix C says "Apply measured or estimated load profiles as "process 
> loads" to reflect the estimated total loads on the plant". If this is 
> the case, then if I add the process loads in addition to my project's 
> loads, I will be double counting the loads, right?
>
> Does this mean I have to create a dummy project building (with no 
> loads) with the proposed district plant to determine the efficiencies?
>
> 2)Does anyone have additional guidance for modeling district energy 
> systems, other than the one of the USGBC? Something with more examples 
> or maybe a case study with actual numbers?
>
> Best regards,
>
> Omar
>
> ___________________________
>
> Omar Katanani
> Senior Sustainability Engineer
>
> Email: omar at ecoconsulting.net <mailto:omar at ecoconsulting.net>
>
> EcoConsulting (Lebanon)
> Nahas Building, 4^th floor
>
> Georges Haddad Avenue
>
> Postal Code: 2028 5806, Saifi District
>
> Beirut, Lebanon
>
> Tel:  +961 (0) 1 971 266
> Mobile: +961 (0) 3 045 045
>
> EcoConsulting (UK) Ltd
> 28 Marshalsea Road
> London, SE1 1HF
> Tel: +44 (0) 20 8144 0015
> Website: www.ecoconsulting.net <http://www.ecoconsulting.net/>
>
> Description: EcoConsulting Membership Logos (low res)
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140107/43027344/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: application/pdf
Size: 21168 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140107/43027344/attachment-0002.pdf>
    
    
More information about the Equest-users
mailing list