[Equest-users] HP Supp Demand
    Grando, John 
    JGrando at cosentini.com
       
    Tue Jan  7 08:53:42 PST 2014
    
    
  
Your infiltration rates are not the same.  Check the LS-C report.  The peak infiltration in your baseline is 443 KBTU/HR on Jan 25th 7 am and your design is 1656 KBTU/HR on Jan 24th at 6 am.  That seems to be your problem for why there is so much supplemental heat.
John Grando BEMP | CEM | LEED AP BD+C | Associate
Phone: 212-615-3705 | Fax: 212-615-3700
jgrando at cosentini.com
Cosentini Associates - A Tetra Tech Company
Two Pennsylvania Plaza - Third Floor - New York, NY 10121
www.cosentini.com<http://www.cosentini.com/>
NOTICE OF CONFIDENTIALITY
This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof.  In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law.  If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission.  Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege.  If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140107/4a2e058c/attachment-0001.htm>
    
    
More information about the Equest-users
mailing list