[Equest-users] Equivalent Full Load Heating Hours
    Dahlstrom, Aaron 
    ADahlstrom at in-posse.com
       
    Wed Jan 15 11:04:07 PST 2014
    
    
  
Or divide the total consumption by the peak hourly value. Both are available by end use from the PS-E / PS-F reports.
Aaron
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Fred Betz
Sent: Tuesday, January 14, 2014 11:26 PM
To: Sandy LaFlamme; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Equivalent Full Load Heating Hours
Sort of. The PS-C report provides the number of hours in 10% increments. You could use that to calculate full load hours.
You could also run an hourly report plotting the part load ratio. Sum the PLR values to get full load hours.
Hope that helps.
Fred Betz  PhD., LEED AP (r)BD&C
Senior Sustainable
Systems Analyst
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI  53719
P: 608.236.1175 | F: 608.238.2614
fbetz at aeieng.com<mailto:fbetz at aeieng.com>  |  www.aeieng.com<http://www.aeieng.com/>
From: Sandy LaFlamme [mailto:slaflamme at veic.org]
Sent: Tuesday, January 14, 2014 8:08 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Equivalent Full Load Heating Hours
Does eQUEST provide equivalent full load heating hours in any of its reports?  If so, where can I find it?  Thanks!
Sandy
Sandra LaFlamme, PE, CEM |  Engineering  |  EFFICIENCY VERMONT
128 Lakeside Ave, Suite 401, Burlington, VT 05401
slaflamme at veic.org<mailto:slaflamme at veic.org>  |  Office: (802) 540-7797 |  Cell: (802) 233-8997
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140115/3bd235e5/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list