>From the outside looking in and not knowing your design requirements,  I would question why your indoor "Cooling" thermostat temperature setpoint is set at 71.6 F?  That seems like a low and extremely precise cooling setpoint to design to?  Also what is your throttling range of your thermostat?  Designing to something so precise would mean that our throttling range would be zero, which is not realistic.
Also take a look at your AHU setup?  Is it blow through or draw through, essentially where does your fan heat get included in the load, before or after the coil?  If the system is draw through the cooling coil has to have a lower coil leaving air temperature to account for the added fan heat.
Hope that helps.
[cid:image001.jpg at 01CCA5C8.288E04E0]
Steven C. Tobin Jr., P.E.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0061
fax 913 345.0617
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Hala Jaber
Sent: Wednesday, January 22, 2014 2:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Fan power calculation
Hey eQuest users,
I have a new challanging  requirement in the appendix G section G3.1.2.8,  its required the supply air-to room air cooling temperature difference is 20 degrees for each HVAC system. Now my question is how can i achieve this if my baseline is system 8 and the chilled water leaving temperature is specified 44 F with return delta t=12,at the same time that in my design the indoor thermostat temp=71.6 F , and the supply cooling temp should be 51.6F,  here when i set this value i got an error in eQuest stating that" the cooling coil leaving temperatures must be at least 6 F higher than  entering water temp" and when i set the cooling supply air temp below 55 F trying to achieve the 20 degree difference, i got this error.
I hope if any one can help,who may face this in baseline model.
Thanks.
Hala Jaber
Sustainablity Design Engineer.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140122/ab50cdc1/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1778 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140122/ab50cdc1/attachment-0002.jpg>
    
    
More information about the Equest-users
mailing list