[Equest-users] Design Supply Air CFM/OSA CFM
    Patrick J. O'Leary, Jr. 
    poleary1969 at gmail.com
       
    Thu Jan 30 04:27:09 PST 2014
    
    
  
or adjust your cfm & related values by dividing by the altitude 
multiplier factor on input so they come out what you expect them to be.  
i.e. 1000 cfm/1.09 = input, output = 1000 cfm.  you also need to check 
your kw outputs in the sv-a report(s) to make sure they're correct, if 
not divide the kw/cfm input by the altitude multiplier on input.
On 1/29/14 7:04 AM, Lincoln Lam wrote:
>
> Tom,
>
> If you go to the Project & Site tab and right-click on Site Data > 
> Properties, go to Altitude and make the value 0.
>
> Lincoln
>
> Lincoln Lam
>
> CEM, CEA, LEED® AP
>
> Senior Energy Engineer
>
> L&S Energy Services, Inc.
>
> 9 Regent Street, Unit 704
>
> Jersey City, NJ 07302
>
> (201) 484-7944
>
> *From:*equest-users-bounces at lists.onebuilding.org 
> [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Tom 
> Mickley
> *Sent:* Wednesday, January 29, 2014 8:05 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Design Supply Air CFM/OSA CFM
>
> eQuesters,
>
> Why does the design flow supply cfm and design ventilation OSA cfm in 
> the summary tab of the system & zone air-side summary report differ 
> from the user defined inputs I use in detailed data edit mode?  Is 
> there a way to make it exact without having to lower the inputs for 
> every system to get desired flow rates in the summary report?  
> Changing each system's flow and making several simulations until I 
> find the right cfm is too time consuming.  Does eQuest automatically 
> account for duct leakage that would skew the numbers?  If so, how do I 
> change it?  Thanks in advance!
>
> Thanks,
>
> Tom Mickley
>
> Mechanical Engineer CEM
>
> The K Company
>
> Cell 330-760-3994
>
> Office 330-773-5125
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140130/a4fca7ea/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list