Michael, I suggest you take the written sequence of operation with a
grain of salt. Many years of experience has proved that just because a
sequence is written down, doesn't mean the actual controls follow it.
Chilled water operation trend logs such as, supply and return loop
temperatures, pump status/speed, etc. would be very helpful diagnosing
your problem. It is possible that there is an OSA temperature cut off
where the chilled water system stops running completely or stops running
to a non-critical area that does not show up in the written sequence.
Another problem could be that the 100% OSA heat exchanger doesn't work
the same in the winter as it does in the summer. Sometimes, if you are
use VAV cooling control, raising the upper temperature limit from 65 F
to 70 F on the WARMEST control will lower winter cooling consumption.
Then there is the variable infiltration rate due to changing OSA
temperature problem. In the end, you may just have to fake something to
get the cooling consumption to match. There are just too many unknown
variables. One of the reasons I avoid the LEED measurement verification
credit.
________________________________
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org]
On Behalf Of Michael Campbell
Sent: Wednesday, July 09, 2014 7:41 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling an Existing Building - Calibrating
toUtility Bills
Hi,
I'm having some trouble calibrating my model to match the utility bills.
The issue I am trying to resolve right now is with the cooling energy.
Below is a table showing the metered chilled water usage for 2013. As
you can see, the usage is minimal in the winter months and much higher
in the summer months. This is a 100% OA laboratory building with fairly
high interior loads due to lab equipment. It is a VAV system with
district chilled water cooling and district steam preheat, and hot water
reheat coils in the VAV boxes. The problem I am having is that my
modeled chilled water usage is much higher in the winter than expected.
I have tried just about everything I can think of without great results.
I have attached the sequence of operations for the HVAC as well as the
modeling files. If someone can take a look, that would be very helpful.
Thanks,
Start Date
End Date
Chilled Water (KTH)
1/1/2013
1/31/2013
55.8
2/1/2013
2/28/2013
62.4
3/1/2013
3/31/2013
63.3
4/1/2013
4/30/2013
140.5
5/1/2013
5/31/2013
395.5
6/1/2013
6/30/2013
721.3
7/1/2013
7/31/2013
1,277.7
8/1/2013
8/31/2013
850.5
9/1/2013
9/30/2013
448.6
10/1/2013
10/31/2013
266.4
11/1/2013
11/30/2013
65.4
12/1/2013
12/31/2013
52.5
Mike Campbell, E.I.T., LEED AP O+M
Sustainability Specialist
Sustainable Solutions Corporation
Office: 610-569-1047 <http://610-569-1047/>
Mobile: 609-923-1743 <http://610-569-1047/>
www.SustainableSolutionsCorporation.com
<http://www.sustainablesolutionscorporation.com/>
Sustainable Solutions Corporation is WBENC and BCorp Certified.
This email message and any attachments are for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure or distribution is
prohibited. If you are not the intended recipient, please contact the
sender by reply email and destroy all copies of the original message and
any attachments.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140709/a91ea3cf/attachment.htm>
More information about the Equest-users
mailing list