[Equest-users] (3) LEED compliance analysis errors - (DBID 190000020000)?
Chris Baker
CBaker at cci-alliance.com
Wed Jul 16 18:37:36 PDT 2014
I think I have this figured out!
I went back to check that all the applicable spaces are conditioned (they are). All my areas with plenums are unconditioned (they are) - I had read on the usergroup
That some users had issues with this.
Then I went in to the space occupancies in detailed edit.
I remembered reading in DOE2 somewhere that the sum of occupancy type areas MUST equal the overall area of the SPC (or space).
In other words, "Sum of Occupancy Type Area: xxxx ft2" must equal the Area: xxxx ft2 over on the left hand side of the "space properties" window.
Apparently some of my occupancy square footages are equal to the VOLUME (ft3) not the area (ft2).....
DOE2 sais if these are not equal it will inevitably give you errors. This explains it.
Pretty basic newb error and I'm not sure how I missed that!
I'm going to recheck all my inputs and try running the compliance analysis again. I'll post back with the results.
-Chris in Alaska
From: Chris Baker
Sent: Wednesday, July 16, 2014 3:29 PM
To: equest-users at lists.onebuilding.org
Cc: Brian Fountain (bfountain at greensim.com)
Subject: (3) LEED compliance analysis errors - (DBID 190000020000)?
I prepared all my compliance inputs in detailed edit and ran my LEED compliance analysis.
The process completed and gave me three error messages.
Error encountered setting data to LAYERS component (x3)...
'901_NRes_EFlr_Layr' imported from library: BDL Symbol not found (DBID 190000020000) evaluation rule: Fetch NRes Floor layers
'901_Res_EFlr_Layr' imported from library: BDL Symbol not found (DBID 190000020000) evaluation rule: Fetch Res Floor layers
'901_SHtd_EFlr_Layr' imported from library: BDL Symbol not found (DBID 190000020000) evaluation rule: Fetch Semi-heated Floor layers
Has anyone seen this before or know what if I'm missing something?
It definitely has something to do with DBID 190000020000 - which must be floor related.
Chris Baker
CCI CAD Drafter
________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140716/77525d1c/attachment.htm>
More information about the Equest-users
mailing list