John,

You can successfully use the photocell control options creating a schedule of the type "multiplier" for exterior direct loads.

Attached is a discussion on the matter with a nested-attached-discussion including some INP examples.

Fractional might work as well - I found multiplier to work for me at one point and didn't look back =).

~Nick



[cid:489575314 at 22072009-0ABB]

NICK CATON, P.E.
SENIOR ENGINEER

Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Monday, July 28, 2014 12:13 AM
To: Equest-users
Subject: [Equest-users] Correct schedule for Outside lights with Photocell

Hi all:

I asked this question before, but did not receive an answer. I am hopeful some can help.

I am setting up an outside light schedule per ASHRAE 90.1 for LEED. It requires that a time clock or a photocell be controlling the outdoor lighting.

Lighting  schedules (Annual, WEEK, and DAY) are required to be ON/OFF to allow the FORCE-OFF configuration for photocell usage.

HOWEVER, to place these lights in EXTERIOR DIRECT LOADS on the electric meter,  THAT input only accepts a FRACTION type of schedule.

How do I "shoehorn" the outside lights into the model with the photocell operation?

Thanks in advance.

John R. Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/6281dbbf/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/6281dbbf/attachment.jpg>
-------------- next part --------------
An embedded message was scrubbed...
From: Nick Caton <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Exterior lighting Sch
Date: Wed, 13 Jun 2012 14:52:01 +0000
Size: 74349
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/6281dbbf/attachment.eml>


More information about the Equest-users mailing list