[Equest-users] Using C-ACTIVITY-DESC in keyword expressions to assign LPD, equipment loads etc.
Maria Karpman
maria.karpman at karpmanconsulting.net
Mon Jul 28 09:52:54 PDT 2014
My vote is to simplify interior geometry as much as possible, as allowed by
App G. In our experience, having too many spaces / zones significantly
increases calculation time, complicates model editing, and makes eQUEST less
stable (i.e. increases likelihood of crashes). Arguably, breaking the actual
HVAC zones into separate spaces based on space type conflicts with App G
Table G3.1 #7 which says that
where HVAC zones are defined on HVAC design
drawings, each HVAC zone shall be modeled as a separate thermal block.
eQUEST assumes that each space is an HVAC zone with its own thermostat / VAV
box, so modeling spaces within a zone may skew results compared to the model
that reflects the actual HVAC zoning.
You can still use expressions that Bill described below for zones with
homogeneous space types or with one predominant occupancy. For example, if
98% of zone area are corridors, and 2% are restrooms, using corridor LPD for
the entire zone in the baseline will have negligible impact on results. For
zones with diverse space types, we typically over-write the user default
(LPD based on activity type) with user expressions like the one below, for a
zone with 60% area taken by corridors, 10% by lobby, and 30% by storage.
(This expression replicates calculations done by eQUEST DD Wizard which
generates zone LPD based on inputs on screens 13 and 14 of the Shell
sequence.)
Maria
--
Maria Karpman LEED AP, BEMP
________________
Karpman Consulting
<http://www.karpmanconsulting.net> www.karpmanconsulting.net
Phone 860.430.1909
41C New London Turnpike
Glastonbury, CT 06033
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Bishop, Bill
Sent: Monday, July 28, 2014 12:19 PM
To: Greenberg, Ari; Singhal, Harshul; Jeff Haberl; wafik adbelkarim
Cc: equest-users at lists.onebuilding.org
Subject: [Equest-users] Using C-ACTIVITY-DESC in keyword expressions to
assign LPD, equipment loads etc.
The space description C-ACTIVITY-DESC, as shown below, can be referenced
by keyword expressions.
For example, to assign LPD by space type, follow these steps:
1. As always, save your project and work from a new copy whenever
trying something that may be hard or impossible to undo if you pull an
oops.
2. Enter consistent space descriptions based on the first four
characters of the description. (Office open and Office Enclosed will
both be treated as offi because the BDL expression mechanism uses four
characters.) This is the most time-consuming step.
3. Enter the following string as a User-Defined Default Expression for
LIGHTING-W/AREA:
if(#RV(#L("LIGHTING-SCHEDUL",0))!=0) then unused
else switch(#L("C-ACTIVITY-DESC"))
case "acti": 0.8
case "clas": 1.4
case "offi": 1.0
default: 1.2
endswitch
endif
(Add or replace case statements, and the default value as applicable to your
projects space types. I kept the DOE-2 default expression in the example
above, and then added the switch statement.)
This appears in the input file as the following:
SET-DEFAULT FOR SPACE
LIGHTING-W/AREA = (
{if(#RV(#L("LIGHTING-SCHEDUL",0))!=0) then unused
else switch(#L("C-ACTIVITY-DESC"))
case "acti": 0.8
case "clas": 1.4
case "offi": 1.0
default: 1.2
endswitch
endif
} )
..
4. Restore default to the LIGHTING-W/AREA values of each space to
apply the values from the keyword expression. You can do this manually by
right-clicking in the field for each space or by deleting lines in the input
file. I use the NoteTab Light text editor and the regular expression
^ LIGHTING-W/AREA.*$ to delete all space LPD assignments (being careful
not to delete the keyword expression just entered above), as follows:
5. Repeat these steps as desired for other keywords, such as
EQUIPMENT-W/AREA, LIGHTING-SCHEDULE, AREA/PERSON etc. Be creative!
6. Do a happy dance.
H/T to Jeremy McClanathan for helping me with this previously.
Regards,
Bill
From: Greenberg, Ari [mailto:agreenberg at CANNONDESIGN.COM]
Sent: Monday, July 28, 2014 11:21 AM
To: Bishop, Bill; Singhal, Harshul; Jeff Haberl; wafik adbelkarim
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] space renaming
Hi Bill,
Using a keyword expression to automatically assign LPD by space type sounds
like a neat trick that would save some time. Would you mind sharing a
little more about how to set this up?
Thanks,
Ari
Ari Greenberg, LEED AP BD+C
cid:image001.png at 01CEFD8A.E416B290
100 Cambridge St., Suite 1400
Boston, Massachusetts 02114
T 617.517.6224 M 857.231.1076
cannondesign.com
http://thinkbeforeprinting.org/struct/signature-1.gif
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Bishop, Bill
Sent: Monday, July 28, 2014 11:07 AM
To: Singhal, Harshul; Jeff Haberl; wafik adbelkarim
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] space renaming
You can easily justify over 100 zones on larger projects (say 50,000 ft2 or
more), especially if they are not multi-story with identical floor plans.
Most of the modeling I do uses Appendix G methodology, where lighting power
density is assigned by space type. I use a keyword expression to assign LPD
based on the space type, as assigned via the C-ACTIVITY-DESC space keyword.
This makes it easy to accurately model LPD and to provide documentation for
LEED submissions. However, it only works if you define zones as the smaller
of the HVAC zone or the space type. (You cant combine a classroom, bathroom
and storage room into one space even if they are effectively one HVAC zone.)
Regards,
Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers &
Architects LLP
Senior Energy Engineer
ASHRAE Certified logo - greenshot 2
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
<mailto:wbishop at pathfinder-ea.com> bbishop at pathfinder-ea.com
<http://www.pathfinder-ea.com/> www.pathfinder-ea.com
earth for signatureSustainability the forest AND the trees.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Singhal, Harshul
Sent: Monday, July 28, 2014 10:50 AM
To: Jeff Haberl; wafik adbelkarim
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] space renaming
I also feel 476 spaces are way too much. I can understand that some projects
have different floor plates & plans and it can end up resulting more number
of zones. But trust me the more number of zones, more complicated it gets. I
did one project with almost 150 zones (multi family high rise building) and
later when I moved to detailed mode it was a pain to make changes for
spaces/zones.
I would suggest rather creating separate zones for same user type spaces
facing same façade, you can combine them as one single zone each floor. For
corner rooms/spaces, create separate spaces. Try to keep it under 100
atleast.
Harshul Singhal
Project Consultant
Thornton Tomasetti
386 Fore Street, Suite 401
Portland, ME 04101
T 207.245.6060 F 207.245.6061
D 207.245.6074
<mailto:HSinghal at ThorntonTomasetti.com> HSinghal at ThorntonTomasetti.com
<http://www.ThorntonTomasetti.com> www.ThorntonTomasetti.com
From: Equest-users [ <mailto:equest-users-bounces at lists.onebuilding.org>
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jeff Haberl
Sent: Monday, July 28, 2014 9:09 AM
To: wafik adbelkarim
Cc: <mailto:equest-users at lists.onebuilding.org>
equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] space renaming
Hello Wafik.
One question you might ask is why you have 476 spaces in EQUEST?
Normally, a space is needed only if that zone has a unique load, usage,
external exposure or HVAC system. Otherwise, it is more common to use a
simplified zoning. For example, 5 zones are normally used for a rectangular
building of more than 50 ft in depth. At most, for a multistory building,
three floors can be used, one for the top floor, one for the middle floors,
and one for the ground floor.
Hence, you might consider reducing the number of zones before proceeding.
Jeff
Jeff S. Haberl, Ph.D., P.E.inactive, FASHRAE, FIBPSA
Department of Architecture
Texas A&M University
College Station, Texas 77845-3581
Office: 979-845-6507, Lab: 979-845-6065
Fax: 970-862-2457, jhaberl at tamu.edu, www.esl.tamu.edu
On Jul 26, 2014, at 3:19 PM, "wafik adbelkarim" <abdelkarim.wafik at gmail.com>
wrote:
good day every body,
what is the fastest and easiest way to rename about 476 space in eQUEST
model.
instead of going one by one then doing the same for the thermal zones!
whats the best way to name both using the wizard without having any errors?
is there is any shortcuts?
regards,
Wafik
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
The information in this email and any attachments may contain
confidential information that is intended solely for the
attention and use of the named addressee(s). This message or
any part thereof must not be disclosed, copied, distributed
or retained by any person without authorization from the
addressee. If you are not the intended addressee, please
notify the sender immediately, and delete this message.
<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4716 / Virus Database: 3986/7910 - Release Date: 07/24/14
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 58955 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 74551 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 65511 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 6945 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 566 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2832 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2181 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3066 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 10709 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 18766 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140728/8c606390/attachment-0003.jpeg>
More information about the Equest-users
mailing list