That was a good thread wasn't it =)? For those interested the thread discussion took place off and on in 2011 and 2012 - I've attached for easier reading (the earlier thread includes many visual curve illustrations).
Guidance here remains FUZZY (to my knowledge & understanding)!
I would clarify/nitpick that 6.5.3.2.2 itself does not require SP reset, rather it specifies how pressure sensors are to be installed when they are in play. The preceding section introduces the idea that part-load control is required, but only for 10hp and larger motors. You may be overly conservative in attempting to apply SP reset to your baseline.
That said, if your proposed design employs good static pressure reset control strategies, I think you are within acceptable territory to differentiate that from the prescribed baseline VAV curve (invoking an exceptional calculation and providing your logic via narrative/writeup), but therein lies the rub: how can you marry the two when the prescribed baseline curve does not appear to recognize realities like motor or VSD losses?
The easy thing to do would be to just match curves and move on, but you're posting in this forum so of course that isn't the answer you're looking for is it ;)?
If I were trying to solve this for a LEED job, I would start with the prescribed baseline curve, and build upon that in a logical fashion, citing and including the EDR guidelines along the way, to come up with an apples-to-apples equivalent curve representative of the "good" practices which result in real world energy savings through proper implementation of SP reset strategies. Then maybe I'd send the report to Popular Science to get published and have a few strangers buy me a beer at the next energy modeling conference... right? right?
Not a lot of direct help here, but assurance that you are on the cutting edge and blazing new paths, as far as I can tell ;).
Best of luck!
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Melissa Crowe
Sent: Thursday, July 31, 2014 1:07 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Fan energy fundamentals - Appendix G models
In this previous thread I am not sure if anyone answered my question. Even if it was answered I can't find it so I'm hoping someone could help.
For a LEEDv9 model (90.1 2007) we use the Appendix G VAV fan curve for the base case model. However, 2007 requires SP reset in 6.5.3.2.2. Can we used the EDR Guide (good SP Reset) curve for the proposed model? Or are we to use App G curve for both cases?
In the past I've used the Good SP Rest for the Proposed but I'm not sure if I've been gaming the system.
Thanks
Melissa
[Description: Description: Description: Description: Description: cid:image003.jpg at 01CCFDCE.40462190]
Melissa P. Crowe, LEED AP
Project Engineer
Engineered Solutions, Inc.
6 Union St, Natick MA 01760
508.647.9200 x225 (P) l 508.652.1936 (F)
MCrowe at EngSolutions.com<mailto:MCrowe at EngSolutions.com>
CAUTION: The preceding email message and any attachments to it may be confidential and/or may contain proprietary information that is entitled to protection from disclosure under applicable law. It is not intended for transmission to, or receipt by, any unauthorized persons. If you are not the intended recipient or such recipient's employee or agent, please do not read any attachments, or print, copy, disseminate or otherwise disclose the contents of this email. If you have received this message in error, please (i) notify the sender by return email immediately that you received the message in error, and (ii) erase or destroy the message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140731/800e0ae4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140731/800e0ae4/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140731/800e0ae4/attachment-0001.jpg>
-------------- next part --------------
An embedded message was scrubbed...
From: Nick Caton <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Fan energy fundamentals - Appendix G models
Date: Fri, 24 Feb 2012 21:49:49 +0000
Size: 285142
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140731/800e0ae4/attachment.eml>
-------------- next part --------------
An embedded message was scrubbed...
From: Nick Caton <ncaton at smithboucher.com>
Subject: Re: [Equest-users] Fan energy fundamentals - Appendix G models
Date: Tue, 11 Oct 2011 19:44:37 +0000
Size: 191227
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140731/800e0ae4/attachment-0001.eml>
More information about the Equest-users
mailing list