Mon May 12 08:24:01 PDT 2014
Hi Sravya,
I’d be a proponent of simply adjusting the zonal heights between your hall zones and room zones, to match averaged ceiling height for each (achieving corrected space volume). This should be a fair approximation. If you do only this in detailed mode I think you’ll end up with “holes” along the rooftop in the 3D view, at each roof elevation change. I would leave as such, as the area for roof conduction should be approximated pretty well in this fashion.
Other thoughts per your 3D view:
- I think you’re missing some sky lights for zone 3,
- Suggesting a shading element to account for the covered balconies, reducing solar loads incident on zone 1. You could do the same to account for the balcony construction below.
- Take note if zones 3/4 as illustrated are modeled with ordinary envelope constructions out of the wizards, your model is dealing with much more exterior exposure to outside conditions.
[cid:image003.png at 01CF6DCA.E111B850]
If you mean to do a prettier job of it in 3D view, with tilted roof sections, you’ve got quite a bit more work ahead of you, and would want to do some zonal height adjustment as illustrated, regardless. See attached discussion for more on how I’d approach adjusting tilt for each surface.
~Nick
[cid:489575314 at 22072009-0ABB]
NICK CATON, P.E.
SENIOR ENGINEER
Smith & Boucher Engineers
25501 west valley parkway, suite 200
olathe, ks 66061
direct 913.344.0036
fax 913.345.0617
www.smithboucher.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sravya lakshmi
Sent: Monday, May 12, 2014 1:18 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Cuved roof in Equest
Hi
I m currently working on a resort and i m trying to make a curved roof for the same .I have tried doing it by taking a pitched roof and changing the co-ordinates for the same.And i have tried doing it in the detailed mode also.But i couldn't make it.I m attaching some of the views of my equest file and section of the roof.so please help me in making the roof.
Thank you
Regards
sravya
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140512/e9faaac7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140512/e9faaac7/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 100795 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140512/e9faaac7/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Equest-.jpg
Type: image/jpeg
Size: 74562 bytes
Desc: Equest-.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140512/e9faaac7/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Section of the building.pdf
Type: application/pdf
Size: 641026 bytes
Desc: Section of the building.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140512/e9faaac7/attachment.pdf>
-------------- next part --------------
An embedded message was scrubbed...
From: Nick Caton <ncaton at smithboucher.com>
Subject: Re: [Equest-users] sloped roof
Date: Tue, 20 Sep 2011 17:44:21 +0000
Size: 53380
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140512/e9faaac7/attachment.eml>
More information about the Equest-users
mailing list