[Equest-users] Pump Power Limit (19W/gpm & 22 W/gpm)
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Nov 3 06:18:14 PST 2014
So, does the ASHRAE interpretation IC 90.1-2007-14 imply that the "gpm" used in the calculation should be only the flow rate of the primary loop (or alternatively, only the secondary loop)? For example, if you have a CHW system with 500 gpm flow in the primary loop and 500 gpm flow in the secondary loop (they are only equal if the loop delta-t is equal), is the "gpm" in "22W/gpm" 500 gpm or 1000 gpm? I have not seen this explicitly defined anywhere.
Thanks,
Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image001.jpg at 01CFF747.17298750] [cid:image002.jpg at 01CFF747.17298750]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Javed Iqbal
Sent: Thursday, October 30, 2014 3:28 AM
To: Bernie Hont
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Pump Power Limit (19W/gpm & 22 W/gpm)
Here is the ASHRAE interpretation on this issue.
Hope this helps!
On Thu, Oct 30, 2014 at 6:08 AM, Bernie Hont <bhont at girard.com<mailto:bhont at girard.com>> wrote:
Thanks, I think I got it. Take the loop flow from the PV-A report for chilled water and condenser water systems, multiply by 22 and 19 respectively, and make sure the sum of pump energies for all pumps on each system matches the allowable.
From: David Eldridge [mailto:DEldridge at grummanbutkus.com<mailto:DEldridge at grummanbutkus.com>]
Sent: Wednesday, October 29, 2014 6:51 PM
To: Bernie Hont; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Pump Power Limit (19W/gpm & 22 W/gpm)
Not quite, I think you are close though - try it this way: use the total plant GPM x W/gpm factor, and that gives your total watts to spread across any number of primary and secondary pumps (even if there was only one of each type). It is up to you to reasonably assign that power between multiple secondary and primary pumps.
As an example, if there are two equally-sized chillers and each has a dedicated primary pump, then each primary pump will have the same W/gpm for its half share of the flow.
If you assigned the secondary pump 15 W/gpm as an example, then 7 W/gpm would be left for each of the primary pumps, based on each pump's own gpm.
Total power and gpm are additive for pumps in parallel, but not W/gpm. W/gpm is additive for the total of the primary and total of the secondary, and should equal 22 W/gpm.
Likewise, assuming two dedicated condenser water pumps, each condenser water pump would have 19 W/gpm for its own share of the total gpm...gpm and total power will be additive, not W/gpm.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bernie Hont
Sent: Wednesday, October 29, 2014 4:49 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Pump Power Limit (19W/gpm & 22 W/gpm)
For systems >300 tons where 2 chillers and therefore 2 primary chilled water and 2 condenser water pumps are present: do the 19 and 22 limits for condenser and chilled water pump energy apply to all pumps together? For example, would I take the W/gpm for the secondary chilled water pump and then add both the W/gpm for the two primary chilled water pumps to get to 22 total? Same for the condenser pumps, the sum of the W/gpm for both pumps should equal 19? This question has been answered numerous times before and the consensus has always been the sum of a single primary and single secondary should equal the limit, but I cannot find an instance where it was answered regarding multiple primary pumps.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141103/f6a1f002/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141103/f6a1f002/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141103/f6a1f002/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 3859 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141103/f6a1f002/attachment.png>
More information about the Equest-users
mailing list