[Equest-users] Excessive cooling capacity and "insufficient heating capability" warnings
Gonzalo Lema
GLema at sumacinc.com
Wed Nov 19 08:07:31 PST 2014
Hi,
I finished my baseline energy model. However, my problem is that the auto-size DX cooling capacity is too high (625 ton) while the proposed design has a 90 ton chiller.
I also had a lot of trouble trying to meet heating load hours, and could only satisfy them by putting air dT=20F in the reheat option. If I put less dT or more dT the unmet load hours increase.
[cid:image001.jpg at 01D003DC.BE98AE70]
The warning continues to appear for most of the zones though (but the unmet load hours is zero):
**WARNING**********************************************************************
ZONE EL1 WSW Zone (fG.z1)
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
SYSTEM S1 Sys (PVAVS)
which supplies the above listed ZONE, has a design heating
coil exit temperature, HEAT-SET-T,(plus any zone reheat)
below its MAX-SUPPLY-T or the ZONE DESIGN-HEAT-T, which
might account for the insufficient heating capability.
ZONE EL1 WSW Zone (fG.z1) has a THERMOSTAT-TYPE
of REVERSE-ACTION, which, when added to the issues listed
in the messages above, will cause excessive underheating.
When fulfilling the heating capacity (with reheat dT= 20F), the cooling capacity raised dramatically. Thus, heating and cooling seem to be correlated, but I can't find why the cooling capacity is so high for a 37230 gross sq ft building.
I have 27 VAV zones in the building
Thanks in advance for your help
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009 (Chicago, USA)
Tel: +1.305.814.8805 (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141119/0e68b3ec/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20969 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141119/0e68b3ec/attachment.jpg>
More information about the Equest-users
mailing list