[Equest-users] Excessive cooling capacity and "insufficient heating capability" warnings
Gonzalo Lema
GLema at sumacinc.com
Thu Nov 20 07:03:27 PST 2014
Hi Julien,
Sorry for that, it was my first question in the forum.
Please find it attached.
Best,
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009 (Chicago, USA)
Tel: +1.305.814.8805 (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613 (Guayaquil, Ecuador)
Tel: + 571.3151985 (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
From: Julien Marrec [mailto:julien.marrec at gmail.com]
Sent: Wednesday, November 19, 2014 11:18 AM
To: Gonzalo Lema
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Excessive cooling capacity and "insufficient heating capability" warnings
Hello,
You should include your inp file or at least the relevant section, it'll be much easier to debug and see which parameter is not set the way it should.
Best,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec<http://www.linkedin.com/in/julienmarrec>
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr<http://www.linkedin.com/in/julienmarrec/fr>
2014-11-19 17:07 GMT+01:00 Gonzalo Lema <GLema at sumacinc.com<mailto:GLema at sumacinc.com>>:
Hi,
I finished my baseline energy model. However, my problem is that the auto-size DX cooling capacity is too high (625 ton) while the proposed design has a 90 ton chiller.
I also had a lot of trouble trying to meet heating load hours, and could only satisfy them by putting air dT=20F in the reheat option. If I put less dT or more dT the unmet load hours increase.
[cid:image001.jpg at 01D004A0.CB3C75C0]
The warning continues to appear for most of the zones though (but the unmet load hours is zero):
**WARNING**********************************************************************
ZONE EL1 WSW Zone (fG.z1)
might have insufficient heating capability.
Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
specified DESIGN-HEAT-T for the calculated peak ZONE load
(see LS-A or LS-B for the ZONE peak load.)
SYSTEM S1 Sys (PVAVS)
which supplies the above listed ZONE, has a design heating
coil exit temperature, HEAT-SET-T,(plus any zone reheat)
below its MAX-SUPPLY-T or the ZONE DESIGN-HEAT-T, which
might account for the insufficient heating capability.
ZONE EL1 WSW Zone (fG.z1) has a THERMOSTAT-TYPE
of REVERSE-ACTION, which, when added to the issues listed
in the messages above, will cause excessive underheating.
When fulfilling the heating capacity (with reheat dT= 20F), the cooling capacity raised dramatically. Thus, heating and cooling seem to be correlated, but I can’t find why the cooling capacity is so high for a 37230 gross sq ft building.
I have 27 VAV zones in the building
Thanks in advance for your help
SUMAC
Gonzalo Lema | Mechanical Engineer | LEED GA
Tel: +1.773.857.7906 Ext 7009<tel:%2B1.773.857.7906%20Ext%207009> (Chicago, USA)
Tel: +1.305.814.8805<tel:%2B1.305.814.8805> (Miami, USA)
Tel: +511.253.5355 (Lima, Perú)
Tel: +593.4.600.0613<tel:%2B593.4.600.0613> (Guayaquil, Ecuador)
Tel: + 571.3151985<tel:%2B%20571.3151985> (Bogotá, Colombia)
glema at sumacinc.com<mailto:glema at sumacinc.com>
www.sumacinc.com<http://www.sumacinc.com/>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141120/4bc0b4d7/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20969 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141120/4bc0b4d7/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Fort Carson.inp
Type: application/octet-stream
Size: 205228 bytes
Desc: Fort Carson.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141120/4bc0b4d7/attachment.obj>
More information about the Equest-users
mailing list