[Equest-users] Appendix G "riding the pump curve"
Maria Karpman
maria.karpman at karpmanconsulting.net
Fri Nov 21 08:47:59 PST 2014
Bill,
As far as I understand G3.1.3.5 stems from the following prescriptive
requirement of 90.1:
6.5.4.1 Hydronic Variable Flow Systems. HVAC
pumping systems that include control valves designed to
modulate or step open and close as a function of load shall be
designed for variable fluid flow and shall be capable of reducing
pump flow rates to 50% or less of the design flow rate.
There is also this example in 90.1 User Manual:
Example 6-LLL-Variable Flow Hydronic System
Q
A hot water system has two-way valves at most coils, but occasional
three-way valves are
provided at the end of branches to ensure flow through them. Does this
design comply
with the Standard?
A
Yes, provided the total flow through three-way valves does not exceed 50% of
design
flow. While these end-of-line valves are allowed, they are not usually
required except
perhaps in very large campus systems. Water piping is generally designed for
water
velocities that are high enough so that the time it takes for chilled or hot
water to leave
the plant and reach the control valve will be seconds or minutes, a small
enough time
that the system will not be "starved" and no discomfort will result. To
minimize energy
use in variable flow systems, limit the use of three-way valves to one or
two to prevent
pump dead heading.
I typically follow the approach that you described on LEED models, but
arguably the minimum flow can be increased to 0.5 based on the above. I am
curious to hear what others think!
Maria
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Bishop, Bill
Sent: Thursday, November 20, 2014 4:32 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Appendix G "riding the pump curve"
I'm reposting my question below as it has been a few days with no reply.
Thanks!
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers &
Architects LLP
Senior Energy Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
<mailto:wbishop at pathfinder-ea.com> bbishop at pathfinder-ea.com
<http://www.pathfinder-ea.com/> www.pathfinder-ea.com
http://png-5.findicons.com/files/icons/977/rrze/720/globe.pngCarbon Fee and
Dividend - simple, effective, and market-based.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop,
Bill
Sent: Wednesday, January 26, 2011 2:33 PM
To: Omar Katanani; equest-users at lists.onebuilding.org
Subject: [Equest-users] Appendix G "riding the pump curve"
To model variable loop flow with a single-speed pump, at least one 2-way
valve is needed in a loop. How are people approaching the requirement for
"riding the pump curve" in HW and CHW loops per G3.1.3.5 and G3.1.3.10? Set
all system/zone valves to 2-way and use the default loop-mimimum-flow ratio
of 0.05?
Thanks,
Bill
William Bishop, PE, BEMP, LEEDR AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 325-6004 Ext. 114 F: (585) 325-6005
wbishop at pathfinder-ea.com www.pathfinder-ea.com
<http://www.pathfinder-ea.com/>
P Sustainability - the forest AND the trees. P
_____
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4765 / Virus Database: 4189/8600 - Release Date: 11/20/14
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141121/64d055bf/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141121/64d055bf/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1644 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141121/64d055bf/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3856 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141121/64d055bf/attachment.png>
More information about the Equest-users
mailing list