[Equest-users] Questions regarding baseline envelope
Chris Baker
CBaker at cci-alliance.com
Sun Oct 12 14:15:20 PDT 2014
Someone please correct me if I’m wrong but that has since been removed in later iterations of the ASHRAE standards
The Latest version of ASHRAE Appendix G is 2013, isn’t it?
G3.1, Section 5 – baseline column item “f” is now labeled “Roof Solar Reflectance and Thermal Emittance” but doesn’t mention to use the existing construction as the baseline.
Keeping that in mind I went back to look in Section 5 to see if it is mentioned anywhere to use existing building envelope constructions as the baseline- when it comes to renovating existing buildings.
Section “b” - Opaque Assemblies states that for new buildings, existing buildings, or additions they all need to conform with the following common, lightweight assembly types an shall match the appropriate assembly maximum U-factors in Tables 5.5-1 through 5.5-8 (we are in climate zone 8).
· Roofs – Insulation entirely above deck
· Above-grade walls – Steel framed
· Floors - Steel Joist
· Opaque door types shall match the proposed design and conform to the U-factor requirements from the same tables.
· Slab-on-grade floors shall match the F-factor for unheated slabs from the same tables.
At this point the project is near completion, actually.
I should note also that no new exterior walls were installed on this building, even the existing window sizing remained (just 1 for 1 swap).
The existing 8” CMU walls are from 1940 or so. The building is historic on Fort Wainwright, Army Base.
All exterior walls did receive new insulated wall furring on the inside and 5-1/2” EIFS buildup on the exterior. The roof received new 10” foam system buildup and new klip-rib style decking throughout.
Using the existing construction as the baseline building envelope would make sense to me because I would think it would give more accurate numbers but that isn’t what I’m seeing in Appendix G.
Chris Baker
CCI CAD Drafter
From: Dahlstrom, Aaron [mailto:ADahlstrom at in-posse.com]
Sent: Monday, October 06, 2014 5:21 AM
To: John Aulbach; Chris Baker; Shaun Martin; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Questions regarding baseline envelope
Chris –
Quick flag, if you’re modeling an existing building for LEED you likely will be permitted to model the existing building envelope constructions prior to the renovation as your baseline constructions.
Check out ASHRAE 90.1-2007/2010 Table G3.1 section 5 – “Envelope” – baseline column, item “f” – “for existing building envelopes, the baseline building design shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated.”
Aaron
Aaron Dahlstrom, PE, LEED® AP
In Posse – A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com<mailto:ADahlstrom at in-posse.com> | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Thursday, October 02, 2014 7:53 PM
To: Chris Baker; Shaun Martin; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Questions regarding baseline envelope
Chris:
That is why I stay in the DD Wizard to building the ASHRAE 90.1 model;, so that all of what you speculate is the easier way comes true.
THEN, I can go to the Detail Edit and put in my lighting watts/sf, any process loads, and outside lights. Done with the BASE model.
NOW I make a copy of the Base, call it Proposed, then make all the changes to make the Proposed model.
In THIS way, I have my Base model NAILED. Most important to those LEED reviewers.
John R. Aulbach, PE
On Thursday, October 2, 2014 4:38 PM, Chris Baker <CBaker at cci-alliance.com<mailto:CBaker at cci-alliance.com>> wrote:
The model is for LEED approval.
The proposed building is done, the baseline building is in progress in equest.
To bring the building into compliance, however, what is the methodology most commonly used for the building envelope in particular when creating the baseline model?
For example, do I need to manually change all exterior walls to “steel framed” above grade walls to be in compliance with table 5.5-8?
Do all of these items need to be “manually” changed to the equivalent on table 5.5-8? Roof & Insulation, Above grade walls & insulation, Floors to steel joist, etc…
And if so, it would be faster to go back into the DD wizard for this, correct?
Thanks!
-Chris
From: Shaun Martin [mailto:smartin at shaunmartinconsulting.com]
Sent: Thursday, October 02, 2014 1:45 PM
To: Chris Baker; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] Questions regarding baseline envelope
Hi Chris,
Your question doesn’t state why you are doing the models. If you want to show code, or LEED etc, compliance then you use Table 5.5.8. If you need to show energy savings, for a utility program incentive or similar need, then you would use existing conditions.
Shaun
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Baker
Sent: Thursday, October 02, 2014 2:04 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Questions regarding baseline envelope
So my proposed building is done. I’m working on my baseline building and a little confused on how to model the baseline building envelope/exterior.
This project is a renovation in climate zone 8. Most of the interior walls remain.
All the original roof structures remain , All exterior walls remain. No new exterior walls were constructed.
All exterior walls received a 5-1/2” EIFS system. All roof structures received 8-1/2” foam system buildup with new 2” klip-rib style metal decking.
The only thing that didn’t remain on the envelope was the existing decking and all windows and doors got replaced.
The proposed building is modeled to reflect all this in equest – it is very close.
The building was a chapel and it will remain a chapel (non-residential/religious worship).
So here’s the question…
In the baseline model, do I model the pre-existing configuration or do I change all the wall systems completely to match Appendix G, table 5.5-8?
Table 5.5-8 sais the exterior walls, above grade, should show steel framed.
Also, with regard to the roof, would the baseline roof need to be modeled as it was originally, taking into account the energy usage that the building would have had without the foam buildup we added.
Or would I need to just go off of table 5.5-8 again? – in my case the baseline would be “insulation entirely above deck” from that table.
OR should I just do parametric runs to tweak the baseline values down to be in compliance??
What would be an acceptable practice given the nature of the renovation and that the existing building remained?
Chris Baker
CCI CAD Drafter
________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.
________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.