[Equest-users] Appendix G Baseline for a Hybrid Fuel Source DHW plant
Dhayanandh Murugan
daya.anandh at gmail.com
Fri Oct 17 07:32:06 PDT 2014
Hi Molly,
In your case Baseline heating should be fossil fuel. For further details
and supporting information please refer LEED Interpretation ID#10285.
Thanks,
Daya
On Oct 16, 2014 9:24 PM, "Molly Curtz" <molly.curtz at arup.com> wrote:
> I'm working on a LEED project where we are considering an
> air-source heat pump domestic hot water plant with gas boiler backup for
> low temperatures where the heat pump capacity drops off. Appendix G of
> ASHRAE 90.1 does not seem to give guidance as to what baseline should be
> used (gas or electric resistance) for such a hybrid system. Has anyone
> encountered this before?
>
> Thanks in advance for any suggestions!
>
> Kind regards,
>
> Molly
>
>
>
>
>
> *Molly Curtz *PE BEMP LEED AP BD+C
>
> Senior Mechanical Engineer
>
>
>
> *Arup*
>
> 719 Second Avenue Suite 400 Seattle WA 98104
>
> *t* +1 206 749 9674 *d* +1 206 493 2234
>
> *f* +1 206 749 0665
>
> www.arup.com
>
>
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup business
> systems are scanned for acceptability of content and viruses
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20141017/aaea79df/attachment.htm>
More information about the Equest-users
mailing list