[Equest-users] LEED 2009 - Commercial Interiors Energy Model Question
Mehmet Okumuş / ERKE
mehmet at erketasarim.com
Tue Sep 16 23:16:48 PDT 2014
Hi Jim,
Please find the comments of GBCI about LEED v2009 CI energy modelling:
The entire building segment served by the common HVAC systems (i.e. chilled
water plant, hot water plant, dedicated outdoor air systems) must be
reflected in the Proposed and Baseline models, as outlined in Step 2 in the
LEED ID+C v2009 Reference Guide. The project segment portion of the
building, including the portion of the building served by the common HVAC
systems but located outside of the LEED project scope, must be modeled
identically in the Proposed and
Baseline models to reflect the existing conditions (i.e. envelope
components, operation schedules, occupancy type, interior lighting power and
controls, HVAC systems, thermal zones, and plug loads). For the project
area, which is the portion of the building included in the LEED project
scope, the Proposed model must reflect the system upgrades that are being
performed as part of the LEED project scope in the actual design, and the
Baseline model must reflect the equivalent Appendix G requirements for each
respective upgrade. Revise the Proposed and Baseline models, as needed, to
reflect the entire project segment served by the common HVAC systems which
serve the project area. Ensure that the project segment, located outside of
the LEED project scope, is modeled identically in each model based on the
existing conditions. In addition, ensure that the project area reflects the
actual design for the system being
upgraded in the Proposed model, and that the Baseline model reflects the
equivalent Appendix G requirements for each system upgrade in the actual
design.
Alternatively, the Alternative Baseline compliance path may be followed. If
following the Alternative Baseline compliance path, the entire project
segment portion of the building, including the portion of the building
served by the common HVAC systems but located outside of the LEED project
scope, must be reflected in the Proposed and Baseline models; however, the
Proposed model must reflect the actual design (for the project area) and
existing components (for the remaining spaces outside of the LEED project
scope), and the Baseline model reflects the Appendix G Baseline modeling
requirements (i.e. envelope, lighting, and HVAC systems) for the entire
segment area of the project (both project area and spaces located outside of
the LEED project scope). If following the Alternative Baseline, indicate
that change within a narrative and provide revised simulation input summary
reports for the Proposed and Baseline model reflecting the changes.
Saygılarımla/Best regards,
mehmetokumuş
msc.mechanicalengineer
LEED AP O+M, LEED for Homes Green Rater
Certified Energy Administrator
ERKE Sürdürülebilir Bina Tasarım Danışmanlık Ltd. Şti.
Kısıklı Mah. Hanımseti Sk. No:5 PK:34692 Üsküdar/İstanbul
t: +90 216 369 73 93 f: +90 216 369 73 96
http: <http://www.erketasarim.com/> www.erketasarim.com e-mail:
<mailto:mehmet at erketasarim.com> mehmet at erketasarim.com
P Please consider your environmental responsibility before printing this
e-mail. Save paper!
From: James Hansen [mailto:jhansen at ghtltd.com]
Sent: Wednesday, September 17, 2014 12:31 AM
To: Jim Paulino; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] LEED 2009 - Commercial Interiors Energy Model
Question
There is an area on the template where you enter project area versus entire
building area (and the savings is pro-rated...or whatever the opposite of
pro-rating is). With a 20-story office building, you probably only need to
see an improvement of 1% building wide (on HVAC consumption) for it to
equate to something greater than 15% for your tenant. I highly recommend
looking at the reference guide for this. There are a couple different ways
you can model the baseline building.
GHT Limited
James Hansen, PE, LEED AP, BEMP
Senior Associate
1110 N. Glebe Road, Suite 300
Arlington, VA 22201
703.243.1200 (main)
703.338.5754 (direct/cell)
<http://www.ghtltd.com> www.ghtltd.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Jim Paulino
Sent: Tuesday, September 16, 2014 5:27 PM
To: equest-users at lists.onebuilding.org
<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] LEED 2009 - Commercial Interiors Energy Model
Question
Does anyone have any experience with energy modeling for LEED 2009
Commercial Interiors credit EA1.3 - Optimize Energy Performance?
We have a client that is going to occupy a single floor of a 20 story office
building and they are putting new HVAC systems in for that floor. The main
AC unit for the floor is a condenser water cooled air handler (commonly
referred to as a SWUD unit) that distributes air to VAV boxes. (the rest of
the building uses a similar system and uses the condenser water loop for
heat rejection)
The LEED manual indicates that the whole building must be modeled, which
would almost seem like any savings from the one floor get diluted by what is
happening on the others.
Thanks for any insight
Jim Paulino, P.E., CxA, LEED T AP
Mechanical Engineer
Associate
<mailto:jim.paulino at hesm.com> jim.paulino at hesm.com
HESM&A, Inc.
<http://www.hesm.com/> www.hesm.com
DIRECT:
(678) 628-2787
"Engineering the Built Environment"
_____
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is the
property of GHT Limited. Unauthorized use, disclosure or copying of this
communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please notify me
immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140917/8d346291/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 8074 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140917/8d346291/attachment.png>
More information about the Equest-users
mailing list