I was just looking into this recently.
For VRF systems, I¡¯ve seen direction to use PSZ, PVVT, and PTAC. PVVT is
the approach endorsed/outlined by the Oregon energy trust in a powerpoint
PDF that has made the rounds here on the lists a few times, and as such is
probably ¡°most suggested.¡± PVVT by distinction can model
variable/multispeed fan control at the terminal level, which may or may not
reflect your actual equipment (depends on make/model). Fan control can also
be made ¡°constant¡± in that regard if need be, as such this may be the most
flexible solution. PSZ stands out from this trio as a zonal system type ¨C
this fact may make it an easier system to consider in relation to a model or
baseline you¡¯ve already substantially developed with a zonal system type.
There is more than one right answer, and it¡¯s worth noting/acknowledging
VRF is fundamentally different in operation than any system type currently
within eQuest.
Review of LG and Mitsubishi¡¯s suggested practices / guidance shows some
slight contradictions. Both notably prescribe system type PSZ, to start,
but Mitsubishi explicitly mentions PVVT and PTAC as viable alternatives as
well. Somewhere along the way I recall reading that energy recovery
elements may be more easily accounted for with PSZ over PVVT¡ can¡¯t recall
the specific source. LG by has produced a library of (air-cooled) curves
specifically for use with modeling variable speed compressors. Mitsubishi
in contrast (perhaps, in response¡ also for air-cooled VRF) asserts it
isn¡¯t critical to explicitly model variable speed compressors to
approximate VRF within eQuest, rather that the PLR/EIR/Capacity curves
furnished by the manufacturer can, together, adequately address performance.
As I understand it, any chosen approach to VRF in eQuest involves
¡°post-processing¡± hourly reports to quantify and sum ¡°free¡±
heating/cooling energies. There is some variance in guidance (between the
energy trust of OR and Mitsubishi) on how to sum those free heating/cooling
energies... both methods appear conservative to my understanding of how VRF
works (summing each hour¡¯s energies in isolation of the preceding hourly
results), but then I am certainly no expert.
~Nick
NICK CATON, P.E.
Senior Engineer
360 Analytics
9750 3rd Ave NE, Suite 405
Seattle, WA 98115
office: 206.557.4732 ext. 205
<http://www.360-analytics.com/> www.360-Analytics.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of ????
Sent: Saturday, September 27, 2014 9:29 PM
To: Equest-users
Subject: [Equest-users] ת·¢£ºThe results of your email commands
Can someone explain why a PVVT is usually chosen to model VRV/VRF?
As we all know, Packaged Variable-volume Variable-Temperature (PVVT) systems
can be used to model VRV/VRF system in eQUEST software, but what I am
confused is why a PVVT system can be used.
Load adjustment in pvvt system is implemented by varying supply air flow and
supply temperature. But in VRv system£¬load adjustment is implemented by
varying refrigerant flow in each coil. There is a significant difference
between the vrv and pvvt system. And l always can not get reasonable result
using this way, the heating energy consumption is always too small.
Can someone explain why a PVVT is usually chosen to model VRV/VRF?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140929/722ff230/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 4429 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20140929/722ff230/attachment-0001.jpeg>
More information about the Equest-users
mailing list