[Equest-users] single zone / multizone
David Eldridge
DEldridge at grummanbutkus.com
Thu Apr 23 16:03:58 PDT 2015
You are correct - in this case the "Multizone" type system has a hot deck and cold deck, and these are combined to produce the air supplied to the zone, so there is simultaneous heating and cooling taking place as you surmised.
A "Multizone System" is not the same as "a system with multiple zones, and which might be VAV."
But to be clear, if you are using a single-zone system in the building as shown below, the fair comparison would be one single-zone AHU per zone, and not one serving all of the zones. If that's not the case, check the unmet load hours for both cases in the AHU summary sheet. That may also be one reason why one case is lower energy use than the other - the zones may need some reheat if supplied from a single AHU.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Mark at nationalglazingsolutions.com
Sent: Thursday, April 23, 2015 5:56 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] single zone / multizone
Importance: High
Good afternoon,
Because I am working in fenestration I hope a mechanical systems expert can help me out. If I have the DD Wizard floor plan as below (core/perimeter default is now 18 zones) - why is the Base Case with Multizone Packaged Units kWh almost 3x the Base Case with Single Zone Packaged Units (both electric reheat)?
What is the reasoning behind the multizone electric being so high? When I dig into the details I see that even with tstats at 60 (and in Hawaii) the multizone has significant space heating whereas the single zone has zero space heating.
At the end of the day, I think A/C savings are overstated because it seems like one version has simultaneous heating/cooling but would like to know the 'why'?
The facts are that it's multizone - so it is what it is ... I just want to learn from this and bring the best solution to my customers.
Thanks and take care
Mark
[cid:image001.png at 01D07DEF.F37214A0]
[Description: NGS_Logo_V2a_New]
Mark A. Carlson, CEM | Engineering Manager, Energy Solutions
Direct: 404.580-4639 | Toll Free: 866.925.2083 x 808
Fax: 866.966.4256 | Mark at NationalGlazingSolutions.com<mailto:Mark at NationalGlazingSolutions.com>
NATIONAL GLASS FILMS & PRINTED GRAPHIC FILM SERVICES
WWW.NATIONALGLAZINGSOLUTIONS.COM
National Glazing Solutions was recognized as being the #1 commercial film dealer in the USA (window film mag sept 2013)<http://www.nationalglazingsolutions.com/2013/10/30/n-g-s-named-1-commercial-film-dealer-in-u-s-a/>
Click here < Tri-Shield Video><http://youtu.be/MOCzzBINFY8> to witness the latest proprietary smash & grab protection system exclusively from NGS
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/6f99d898/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 24661 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/6f99d898/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3053 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150423/6f99d898/attachment.jpg>
More information about the Equest-users
mailing list