[Equest-users] Question - Final parametric runs for building rotations
Cam Fitzgerald
cam at energyopportunities.com
Fri Feb 13 04:53:56 PST 2015
Good morning, Cris,
You said your project is a renovation. If the project is at least 50%
existing building, you should not rotate the Baseline case (see Table
G3.1#5(Baseline)(f) which states that the building is modeled as it exists).
Cam Fitzgerald
Energy Opportunities/a 7group company
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On
Behalf Of Chris Baker
Sent: Thursday, February 12, 2015 8:01 PM
To: equest-users at lists.onebuilding.org
Cc: Nick Caton (ncaton at smithboucher.com)
Subject: [Equest-users] Question - Final parametric runs for building
rotations
I'm a first time equest modeler.
I'm trying to finish a model for a renovated building for LEED submission
(LEED Online).
I have the proposed and baseline models done at this point.
My proposed building was created first in DD wizard, I then did all the
compliance inputs manually in detailed edit, and made sure my utility unit
rates were all accurate for my state, everything good to go.
I should note that I did have some problems running LEED compliance analysis
in equest version 7163 (which for some reason involved a specific below
grade wall component). When I opened the model and ran compliance analysis
in equest version 7154 everything worked great so I've been using it ever
since.
I later found out that a lot of modelers create the baseline model first,
but I did the proposed first in this case because I went through each
process in the user guide's DD wizard section (maybe I just misunderstood
the process).
I ran a successful compliance analysis on the proposed model.
When this is done, equest says:
"LEED Analysis Completed. Generation of the LEED baseline building model
was successfully completed. The following baseline design project includes
parametric runs for each building rotation for your convenience in
performing those simulations" - followed by the name of the PD2 file the
baseline is saved as.
I've gone back to the both proposed and baseline models and have verified
all systems and inputs are exactly dialed in the way they should be - with
some amazing, insightful help from Nick Caton, Brian Fountain and others
throughout the process, I should add.
My baseline building is now done and I want to do the final parametric runs
to simulate the building rotations.
Question - Does the message just mean the parametric runs for each rotation
are configured in the baseline model and just need the simulations run?
What is the normal way to proceed from this point?
Chris Baker
CCI CAD Drafter
_____
CCI-Alliance Confidentiality notice: This message is intended only for the
person to whom addressed in the text above and may contain privileged or
confidential information. If you are not that person, any use of this
message is prohibited. We request that you notify us by reply to this
message, and then delete all copies of this message including any contained
in your reply. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150213/64abd459/attachment.htm>
More information about the Equest-users
mailing list