Hi Julien,
Forgot to mention this, I've noticed this too... We've looked a number
of work-arounds but unfortunately I am also under a deadline and don't
have time to go track down what we have been doing lately...
Here are a a few work-arounds that I recall looking at.
1. Use larger HEAT-SIZING-RATIs to get capacities up
2. Specify equivalent infiltration at the Space, but set the
infiltration schedule to 0 on all days/hours other than the design
days. This requires some coordination with the design day windspeed
if you are modeling the wind-speed proportional infiltration that I
mentioned, otherwise, pretty straight-forward if you are using the
constant infiltration input.
Will try to dig up more definitive information later today when I have time.
David
PS: That info on the HRV modeling is also included in the help for
EXHAUST-SOURCE = BALANCED-INFIL. This approach seems like a reasonable
work-around for unit-by-unit HRV/ERVs.
On 2/20/2015 7:45 AM, Julien Marrec wrote:
> Nathan,
>
> Thanks for the answer. Your baseboard workaround is interesting, I'm
> curious whether it produces differences or not.
>
> I'm not using baseboards. I have both UVT systems (gas furnace) for my
> heated-only spaces as well as PTAC (hot water coil / DX cooling coil)
> for the apartments, and both are behaving the same way.
>
> I've played around a little bit, switching between Zonal Exhaust and
> Outside Air Flow. It's not taking the airflow into account when it's
> set as Zonal Exhaust, see attached pictures (Tenant Storage is a UVT
> with 400 CFM exhaust, 2Sys is a PTAC with 41.6 CFM exhaust)
>
> I don't know what to do...
> Aside from running the model with it as Outside Air Flow, writing down
> the sizing, going back to the model to put it back as zonal exhaust
> and manually setting the sizing... I'd do that if I had only a couple
> of zones... But I don't, so it seems highly unpractical.
>
> Anyone has ideas?
>
> Thanks,
> Julien
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> <http://www.linkedin.com/in/julienmarrec>
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
> <http://www.linkedin.com/in/julienmarrec/fr>
>
> 2015-02-20 16:33 GMT+01:00 Nathan Miller <nathanm at rushingco.com
> <mailto:nathanm at rushingco.com>>:
>
> Julien,
>
> I don’t have time to dig into your questions at this moment
> (deadlines!), but just a quick check for you, are you modeling
> electric resistance heat via the system-> baseboards entries? If
> so, I don’t believe eQUEST ever autosizes baseboard heat, you
> always have to manually input (or use a formula based on space
> square footage…).
>
> To get around this I often use the PTAC system, zero-out the
> fanpower, and then select electric resistance heat as the primary
> system level heat source. eQUEST should autosize that for you, and
> it would seem to be a thermodynamically similar system to
> inputting via-base-board (though I’m sure somebody can point out
> why it is better to use baseboards).
>
> **
>
> *Nathan Miller, PE, LEED AP BD+C**– */Mechanical Engineer/Senior
> Energy Analyst/**
>
> *RUSHING*| *D*206-788-4577 |*O*206-285-7100
>
> *www.rushingco.com <http://www.rushingco.com/>***
>
> *From:*Julien Marrec [mailto:julien.marrec at gmail.com
> <mailto:julien.marrec at gmail.com>]
> *Sent:* Friday, February 20, 2015 7:14 AM
> *To:* David Reddy
> *Cc:* Nathan Miller; equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] Exhaust fans in appartment
>
> Hi again,
>
> After implementing zonal exhaust, I'm still in a bit of a pickle.
> For those familiar with it, I'm actually modeling a building per
> the ENERGY STAR MultiFamily High-Rise Simulation Guidelines,
> slightly modified because it may go for NYSERDA Multifamily
> Performance Program (MPP). MPP New Construction, in its v6
> version, has a different calculator that the MFHR one for
> infiltration, and you have to model infiltration and local exhaust
> separately.
>
> Anyway, the calculator is telling me to put:
> - 0.08 ACH in the space with hourly fraction at 0.5 (so 0.04
> ACH...): it's doing some kind of calculation to come up with 0.04
> CFM/sqft of exterior above grade surfaces (roof + ext walls)) that
> leads to the 0.08 ACH figure.
> - Model the exhaust as about 40 CFM per apartment with a fraction
> of always 1.
>
> I don't know why, but this seems fairly low to me (0.38 ACH would
> seems about right for a fairly tight building when you consider
> that building-wide, but here I'm only entering it for the
> apartments right now).
> What do you think?
>
>
> Ultimately, I have one major problem: the heating consumption
> reported is abnormally low. I've been banging my head since
> yesterday trying to figure out why. I think I've ruled out pretty
> much everything (but I'm confident that missing something is
> possible) aside from this ventilation thing.
>
> If I add (or increase) Zonal exhaust to a zone:
> - The attached system sizing doesn't seem to change
> - but suddenly I'm getting unmet heating hours...
> - And I do have *some* more consumption
> *This make me think eQuest somehow doesn't really take zonal
> exhaust into account when autosizing *(but does for consumption)*.
> Do you have the same experience with it? Any workaround to avoid
> this problem?*
>
> Finally, I think I'm in dire need of a pair of experienced yet
> fresh eyes... I'd be extremely grateful if someone was willing to
> take a look at my model. Ping me and I'll send you the file, and
> hopefully return the favor soon.
>
> Thanks a bunch,
>
> Julien
>
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13 <tel:%2B33%206%2095%2014%2042%2013>
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> <http://www.linkedin.com/in/julienmarrec>
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
> <http://www.linkedin.com/in/julienmarrec/fr>
>
> 2015-02-20 13:04 GMT+01:00 Julien Marrec <julien.marrec at gmail.com
> <mailto:julien.marrec at gmail.com>>:
>
> Thanks to both of you for your answers!
>
> David,
>
> You say its combined in quadrature. Is there documentation
> somewhere about this?
>
> Also, I'm confused about how it's more flexible to add HRVs
> when using zonal exhaust. I thought the core principle of
> Zonal Exhaust was that it was directly exhausted to outside,
> which means not going to the central system and thus
> completely bypassing any Heat recovery.
> From the help file: "The SYSTEMS program simulates heat
> recovery from central exhaust only, not from zone exhaust. If
> heat is to be recovered, zone exhaust should not be entered
> but rather allowed to default to the central system."
>
> Am I missing something?
>
> Thanks,
>
> Julien
>
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13 <tel:%2B33%206%2095%2014%2042%2013>
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> <http://www.linkedin.com/in/julienmarrec>
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
> <http://www.linkedin.com/in/julienmarrec/fr>
>
> 2015-02-19 20:35 GMT+01:00 David Reddy
> <david at 360-analytics.com <mailto:david at 360-analytics.com>>:
>
> I agree with Nathan's recommendation; that is also how
> we have also settled on modeling whole house exhaust
> ventilation. With regards to infiltration, we do model a
> nominal amount that is calculated using PNNLs infiltration
> modeling guidelines and is input at the space as the
> component adjusted with wind speed. The EXHAUST-SOURCE =
> infiltration will automatically combine the space and zone
> exhaust in quadrature, which we believe is appropriate, at
> least with respect to what is readily available in
> Doe-2. The space component is assumed the same in
> proposed/baseline unless the intent of the analysis is to
> illustrate the impacts of reducing uncontrolled air leakage.
>
> In addition to other noted flexibility, it is also easier
> to incorporate modeling of variable flow and even HRVs.
>
> -David
>
>
>
> On Thursday, February 19, 2015, Nathan Miller
> <nathanm at rushingco.com <mailto:nathanm at rushingco.com>> wrote:
>
> We model that type of system all the time, and prefer
> to model the outside air as zonal-exhaust (infiltration).
>
> The primary reason is that it ensures the space
> conditioning system sees the same vent load regardless
> of if you switch systems types (or have different
> systems in a baseline vs. proposed case for example).
> On jobs where I input it as OA on systems, I was never
> able to get the ventilation load energy use to line up
> when I compared, for example, electric resistance heat
> to PTACs, probably due to the slightly different
> algorithms employed for each system type.
>
> The other nice thing is that it allows you to model
> the space conditioning fans as cycling to meet the
> load (schedule = 0 all the time, night-cycle-control
> allowed, fan operation = intermittent). If you
> introduce the outside air through the system inputs,
> often it will force the mechanical system fans to
> operate all the time to provide ventilation, but in
> your case, you already have the whole-house-fan to do
> that.
>
> I believe any infiltration air assigned at the zone
> gets tacked on to infiltration air assigned at the
> space. If you want greater control of the net
> infiltration air, you’d probably have to do some math
> and decide when those values should stack, and when
> they would be “double counting” infiltration.
>
> **
>
> *Nathan Miller, PE, LEED AP BD+C**– */Mechanical
> Engineer/Senior Energy Analyst/
>
> *RUSHING*| *D*206-788-4577 |*O*206-285-7100
>
> *www.rushingco.com <http://www.rushingco.com/>*
>
> *From:*Equest-users
> [mailto:equest-users-bounces at lists.onebuilding.org]
> *On Behalf Of *Julien Marrec
> *Sent:* Thursday, February 19, 2015 11:44 AM
> *To:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* [Equest-users] Exhaust fans in appartment
>
> Hi,
>
> I'm modeling an apartment building that has toilet and
> bathroom exhaust, and mechanical supply. Make-up air
> comes from trickle vents.
> (Side note: the corridor has mechanical supply, much
> higher than 62.2 at 0.6 CFM/ft², and no exhaust
> whatsoever, so I expect /some /makeup air would come
> from there too, but I'm prohibited to capture this
> effect...)
>
> I have been thinking about the best way to do this:
> whether I should assign this to a zonal exhaust fan
> (EXHAUST-FLOW) or whether I should specify the CFM
> exhausted as an outdoor air flow (OUTSIDE-AIR-FLOW).
>
> I think the OUTSIDE-AIR-FLOW would be the least
> problematic if I only had to deal with the baseline,
> but in my proposed building I only have baseboards for
> heating, so this wouldn't work.
>
> First, Am I correct in the above statements?
>
> Second, if I do specify an exhaust fan in the
> following way:
> FAN-CONTROL = CONSTANT-VOLUME
> EXHAUST-FLOW = 50
> EXHAUST-FAN-SCH = "Fraction Always 1 Yr"
> EXHAUST-SOURCE = INFILTRATION
>
> (I'm also defining exhaust systems like this for
> mechanical rooms in my basement)
>
> Will eQuest actually take into account that it (he?)
> should add 50 CFM of outside air (through
> infiltration) as a load? Will eQuest also take that
> into account for the sizing of my zonal equipment?
>
> Finally, will it interact in any way with the
> infiltration defined under Internal Loads for the Space?
>
> Thanks for any clarifications you can offer.
>
> Best,
> Julien
>
> --
> Julien Marrec, EBCP, BPI MFBA
> Energy&Sustainability Engineer
> T: +33 6 95 14 42 13 <tel:%2B33%206%2095%2014%2042%2013>
>
> LinkedIn (en) : www.linkedin.com/in/julienmarrec
> <http://www.linkedin.com/in/julienmarrec>
> LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr
> <http://www.linkedin.com/in/julienmarrec/fr>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150220/69f87197/attachment.htm>
More information about the Equest-users
mailing list