Hi all,
In reviewing the results of various models using the GLASS-TYPE-CODE 
method to model windows in eQUEST, we re-stumbled upon a bug that others 
have identified in the past:
http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/2005-June/031299.html
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2012-October/036262.html
We found this issue still exists when generating custom codes using 
WINDOW 6.3/eQUEST v3.64, but in v3.65, it appears that the FILMS-COND 
keyword is now being defined. I have not confirmed that the FILMS-COND 
values are appropriate for various WINDOW generated glazing 
configurations, but they are in the same range as other DOE-2 library 
configurations, the LV-H reported U-COG matches that listed in W6.3.
Just wanted to bring this issue to light again so others are aware of 
this and report that it looks like the bug has been fixed in v3.65!
-David
-- 