[Equest-users] Pump/Dump Chillers
    David Eldridge 
    DEldridge at grummanbutkus.com
       
    Wed Jan  7 17:48:45 PST 2015
    
    
  
1.       Look for "Lake/Well" type chiller. You may have to configure some "dummy" loads as eQUEST may be expecting there to be both a CHW and HW load for this type of chiller...after another recent discussion I'm not sure if you can run with CHW loads only.
a.       Depending on your water temperatures in this location you might be able to simulate it by using "magic" condenser water pumps and "magic" cooling towers with 0.0 EIR. You'll still be limited by the ambient wetbulb on what water temperature you can achieve, even with minimized approach temperatures - the Lake/Well option will give you the most control over the water temperatures you need.
2.       You'll need to have some archiving tool on your PC to achieve recovery of your input files, eQUEST does not include any backup capabilities.
a.       One possibility is if you ran the old model and saved over the input files - but didn't run the new model - then there might be some output files left over that you can extract some information from to recreate inputs. Look for "filename.BDL" and open it in notepad or viewer of your choice if you have it in your directory from a failed simulation. Otherwise maybe you can glean something from the other output files to help you reconstruct.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Grumman/Butkus Associates
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Tom Mickley
Sent: Wednesday, January 07, 2015 11:40 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Pump/Dump Chillers
Two questions...
1)      Is there a way to model a pump and dump chiller in eQuest version 3.64?  The chiller I am trying to model rejects the condenser water heat by pumping city water through the barrel and dumping back into the sewer afterwards.  I'm pretty sure this chiller is from the Mesozoic era.
2)      I was trying to be on the safe side and make a backup copy of a model.  However, I accidentally saved over the wrong file and lost a lot of work.  Is there a way to revert back in time in eQuest to bring back a previous model?  Something tells me I might be up a creek on this one.
Thank you all in advance.
Thanks,
Tom Mickley
Mechanical Engineer CEM
The K Company
Cell 330-760-3994
Office 330-773-5125