[Equest-users] Enthalpy wheel with evaporative cooling on the exhaust air stream
    Nicholas Caton 
    ncaton at catonenergy.com
       
    Fri Jan  9 17:18:02 PST 2015
    
    
  
Hi Chris!
So… fancy swamp cooler eh? (j/k)
A system of this description came up once on the lists (see attached
initial post with INP and following discussions), though I don’t see any
explicit answers provided on a cursory search.
I’d also be inclined to first explore the limitations of the existing
evaporative cooler system type to see if you might be able to end up with a
fair approximation… looks like an economizer is an option for standalone or
add-on units (suggest checking out the DOE2 entry for EVAP-CL-AIR and
EVAP-CL+REC-RA – cited figures are copied below), but no configuration
places the cooler directly ahead of the wheel, rather parallel or
downstream… would this be a pretty bad stretch?   Consider you can
optionally specify the return air stream as the secondary airstream for an
indirect cooler (not as pictured below with outside air for the secondary).
*NICK CATON, P.E.*
*Owner*
*Caton Energy Consulting*
  1150 N. 192nd St., #4-202
  Shoreline, WA 98133
  office:  785.410.3317
www.catonenergy.com
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
Behalf Of *Haddad, Kamel
*Sent:* Friday, January 09, 2015 12:13 PM
*To:* Jones, Christopher; equest-users at lists.onebuilding.org
*Subject:* Re: [Equest-users] Enthalpy wheel with evaporative cooling on
the exhaust air stream
Chris, There is an evaporative cooling system in eQ. Couldn’t you connect
this system to a system with the enthalpy wheel using the “Outside air
from” option?
*From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
<equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Jones,
Christopher
*Sent:* January 9, 2015 10:29
*To:* equest-users at lists.onebuilding.org
*Subject:* [Equest-users] Enthalpy wheel with evaporative cooling on the
exhaust air stream
I have a project that has no direct cooling but has an enthalpy wheel and
evaporative cooling on the exhaust air stream before the heat wheel.  Has
anyone come across this arrangement and has anyone figured out a work
around for equest?
*Christopher Jones**,* P.Eng.
Tel: 416.644.4226 • Toll Free: 1.888.425.7255 x 527
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain
confidential information for the sole use of the intended recipient(s). Any
unauthorized use, disclosure, viewing, copying, alteration, dissemination
or distribution of, or reliance on this message is strictly prohibited. If
you have received this message in error, or you are not an authorized
recipient, please notify the sender immediately by replying to this
message, delete this message and all copies from your e-mail system and
destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150109/dc5178a6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 50099 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150109/dc5178a6/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 48616 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150109/dc5178a6/attachment-0001.png>
-------------- next part --------------
An embedded message was scrubbed...
From: unknown sender
Subject: no subject
Date: no date
Size: 3255954
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150109/dc5178a6/attachment.eml>
-------------- next part --------------
An embedded message was scrubbed...
From: unknown sender
Subject: no subject
Date: no date
Size: 30675
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150109/dc5178a6/attachment-0001.eml>
    
    
More information about the Equest-users
mailing list