Nick,
Click on “Credit Library” in prerequisite:
[cid:image003.jpg at 01D03739.11AC6A40]
Then “Resources”:
[cid:image005.jpg at 01D03739.11AC6A40]
Then “Minimum Energy Performance Calculator”:
[cid:image011.jpg at 01D03739.11AC6A40]
Then “Download” and you’ll get attached spreadsheet:
[cid:image012.jpg at 01D03739.11AC6A40]
Mark Zoeteman, PE, CEM, HBDP, LEED AP O+M • Senior Mechanical Engineer • 616-464-3739 • www.ftch.com<http://www.ftch.com/>
Fishbeck, Thompson, Carr & Huber, Inc. • engineers, scientists, architects, constructors
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton
Sent: Friday, January 23, 2015 6:10 PM
To: Nathan Miller; Cam Fitzgerald; Paul Diglio; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline DOAS for LEED
Not to derail, but a related tangent:
1.        I cannot find the familiar short hyperlink list of downloadable EAp2 “credit resources” under the revamped LEED Online site... does this still exist and if so can anyone walk me through navigating there?
2.       What I did find, clicking around LEED Online while logged in, was a link suggesting this particular resource (and the older version at that!) is supposed to cost $120 ($100 for USGBC members): http://www.usgbc.org/resources/advanced-energy-modeling-leed-technical-manual
That isn’t a print copy, either…
I’ve collected 2 versions of the “Advanced Energy Modeling for LEED 2009” technical manual in my references over the years… I don’t recall paying for them (and some cursory googling shows they can still be easily found without cost)… Is this a different resource or am I an unwitting pirate?
~Nick
NICK CATON, P.E.
Owner
Caton Energy Consulting
  1150 N. 192nd St., #4-202
  Shoreline, WA 98133
  office:  785.410.3317
www.catonenergy.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Nathan Miller
Sent: Tuesday, January 20, 2015 6:47 AM
To: Cam Fitzgerald; 'Paul Diglio'; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Baseline DOAS for LEED
I would second that thought. I’ve worked on projects where a gas-fired unit provides neutral air (DOAS) to apartment unit WSHP or VRF. You start getting into some weird warping of results if you compare that system to PTAC or PTHP baseline (heat pump heating uses less site energy than furnace heating, but natural gas tends to have much lower energy cost). Anyway, in the past I’ve successfully argued that G3.1.2.3 provides the basis that the tempering system should be modeled in the proposed case, thus you get more of an apples-to-apples comparison (gas unit picks up the vent load, heat pumps pick up the skin load).
G3.1.2.3 Preheat Coils. If the HVAC system in the proposed design has a preheat coil and a preheat coil can be modeled in the baseline system, the baseline system shall be modeled with a preheat coil controlled in the same manner as the proposed design.
I concede that a gas-fired furnace IS NOT a preheat coil, but it is essentially serving the same purpose in many cases (heat pumps can’t handle the incoming temp of the OA if it was delivered directly to the units…). At any rate, the GBCI reviewers have accepted this rationale in the past, but it in no-way ensures they will rule that way in the future.
As Cam points out, don’t double count fan energy. The 0.3 W/CFM for PTHP/PTACs is total system fan energy, and in the projects I worked on I zeroed out the fan power on the baseline DOAS unit.
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 | O 206-285-7100
www.rushingco.com<http://www.rushingco.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Cam Fitzgerald
Sent: Tuesday, January 20, 2015 8:19 AM
To: 'Paul Diglio'; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Baseline DOAS for LEED
Paul,
I didn’t see a response to your question. Although I cannot address the issues raised by your reviewer, you may find it helpful to review the Advanced Energy Modeling for LEED 2009 (free resource available under project resources in LEED online). Table 3.1 under “Common Errors “addresses this issue (page 33 in the September 2011 edition, 4th bullet) which includes an exception for high-rise residential projects in hot, humid climates. Note that this exception still prohibits any extra fan power for this additional system in the Baseline case. Since your VRF units will typically have very low fan power, the penalty for the additional ventilation system fan power should be minimized and easily recaptured by other efficiency improvements in the design.
Hope this helps,
Cam Fitzgerald
Energy Opportunities/a 7group company
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Diglio
Sent: Friday, January 16, 2015 9:32 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Baseline DOAS for LEED
Hi Folks:
I submitted a model to LEED of a 7 story apartment building.  In the proposed design a DOAS was specified because natural ventilation could not be provided per 62.1 due to the dimensions of the apartments.
Another issue is that the HVAC systems are Daikin VRF and they could not be supplied with directly ducted outside air due to the installation locations and the VRF cassettes do not have a fitting for an outside air duct.
The GBCI came back and said I could not include the DOAS in the baseline model.  The baseline HVAC system per 90.1 requirements are PTHP.  I responded to them twice with various reasons the DOAS needed to be included in the baseline but they won't budge.
Has anyone successfully addressed this type of design?
Thank you,
Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
203-415-0082
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150123/6bd235c4/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 4133 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150123/6bd235c4/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 6602 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150123/6bd235c4/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 13306 bytes
Desc: image011.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150123/6bd235c4/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.jpg
Type: image/jpeg
Size: 15308 bytes
Desc: image012.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150123/6bd235c4/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Minimum Energy Performance Calculator.xlsm
Type: application/vnd.ms-excel.sheet.macroenabled.12
Size: 454656 bytes
Desc: Minimum Energy Performance Calculator.xlsm
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150123/6bd235c4/attachment.bin>
    
    
More information about the Equest-users
mailing list