[Equest-users] Problem with Sage Glass Analysis
David Reddy
david at 360-analytics.com
Wed Jul 22 13:28:27 PDT 2015
As others have indicated, yes, this can be modeled in eQUEST.
Rather than using the library file provided by a vendor, we created our
own G-T-C descriptions using the WINDOW 6 program and importing into
eQUEST. We found some interesting bugs/constraints that I think might
help reduce some headache for others, and in the case of #1, give more
realistic results. Haven't reviewed the materials provided by Josh to
see if these are now addressed in the directions provided by Sage Glass,
though I did forward this to them earlier this year when we discovered them.
1. In eQ v3.63 and 3.64, the import of WINDOW data neglected to
populate the FILMS-COND keyword when creating the custom
GLASS-TYPE-CODE (G-T-C). This resulted in much lower U_cog values
than expected. We tested import with v3.65 and this bug appears to
have been fixed.
2. If used for switchable glazing, the GLASS-TYPEs referenced by WINDOW
objects must be listed in the input file in consecutive order.
Otherwise, a BDL error will result.
3. If used for switchable glazing, the G-T-Cs used must have an numeric
integer name that is >1000. Otherwise, a BDL error will result.
Hope this helps,
David
On 7/22/2015 1:07 PM, David Griffin II wrote:
>
> I received the attached files from Sage Glass for my eQUEST model.
> Contact Josh – see below- for additional information.
>
> **
>
> *Josh Battles*, *LEED Green Associate* * | *Architectural Solutions
> Manager | o:507-331-4921 c:507-323-5626 | josh.battles at sageglass.com
> <mailto:josh.battles at sageglass.com>
>
> www.sageglass.com <http://www.sageglass.com/> | 2 Sage Way |
> Faribault, MN 55021
>
> Sincerely,
>
> ARCH | NEXUS <http://www.archnexus.com>
> DAVID W. GRIFFIN II
> BEMP
> ENERGY ANALYST
> 2505 E Parleys Way
> Salt Lake City, UT 84109
> *Office* 801.924.5028
> archnexus.com <http://www.archnexus.com>
> Twitter <https://twitter.com/arch_nexus>Facebook
> <https://www.facebook.com/pages/Architectural-Nexus/179588705397563?ref=ts&fref=ts>Youtube
> <https://www.youtube.com/channel/UCYRPWKF-yp-AUiI8ia2XfKw?feature=mhee>LinkedIn
> <https://www.linkedin.com/company/architectural-nexus>
>
> *From:*Brian Cline [mailto:briancline at u.boisestate.edu]
> *Sent:* Tuesday, July 21, 2015 4:32 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Problem with Sage Glass Analysis
>
> Hi,
>
> I am attempting to model energy saved by installing electrochromic
> glass for use in a large west facing lobby area into eQUEST. Given
> that eQUESTS capabilities only include modeling a single tint for a
> pane of glass in a shell, how would I go about analyzing electricity
> consumption with the electrochromic glass for each hour over the
> course of a year? If anybody either has thoughts on this or has done
> this in the past, I would sure appreciate it.
>
> Thanks,
>
> -Brian Cline-
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150722/0ca9ef3e/attachment.htm>
More information about the Equest-users
mailing list