[Equest-users] Thermal mass effects
Keith Swartz
KSwartz at seventhwave.org
Wed Jun 3 14:03:02 PDT 2015
Peter,
There are two ways to model walls (and roofs) in eQUEST. To capture thermal mass effects you have to use the layer-by-layer input. Using resistance only will not account for thermal mass.
Keith Swartz, PE
Senior Energy Engineer | Seventhwave | Madison.Chicago.Minneapolis
(formerly Energy Center of Wisconsin)
608.210.7123 | www.seventhwave.org<http://www.seventhwave.org/>
From: bfountain at greensim.com [mailto:bfountain at greensim.com]
Sent: Wednesday, June 03, 2015 1:37 PM
To: 'Peter Schonherr'; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Thermal mass effects
External shades can be modelled as “Fixed Shades” in the detailed mode.
Solar gains are indeed modelled. Have a look at the summary view for a wall construction to see the impact of changing thermal mass: [cid:image001.jpg at 01D09E16.BC962510]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Peter Schonherr
Sent: June-03-15 10:30 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Thermal mass effects
Hello,
I am new to eQuest. I am trying to model the effects of thermal mass in the external walls on space conditioning efficiency. Does eQuest take into account solar gain on the building walls? Why I ask is that I've noticed that increasing thermal mass in the walls, (while maintaining the same R-value), has no effect on the heating load and very little on the heating demand. I also noticed that there doesn't seem to be a way to specify external shading from trees, adjacent buildings, etc.
Peter
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150603/7348b96b/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 68955 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150603/7348b96b/attachment.jpg>
More information about the Equest-users
mailing list