[Equest-users] Modeling air-side economizer
Chris Baker
CBaker at cci-alliance.com
Wed Mar 4 10:53:02 PST 2015
Sami,
Thanks for your reply.
What would be the best approach in your opinion?
I could technically model as different system type (packaged single zone, etc.). And apply cooling per the economizer schedule to the existing systems individually.
That way the system is accurately modeled.
OR I could keep the system as it is now, with unit ventilator, and add a separate stand-alone economizer system that would apply to all the zones.
Thank you!
-Chris
From: Sami, Vikram [mailto:vikram.sami at zgf.com]
Sent: Wednesday, March 04, 2015 8:33 AM
To: Chris Baker; equest-users at lists.onebuilding.org
Subject: RE: Modeling air-side economizer
This is probably happening because the System type: Unit Ventilator is a heating only system (so in essence you are always in economizer mode - there is no cooling modeled).
Vikram Sami
AIA, BEMP, LEED BD+C
Associate Partner
ZGF ARCHITECTS LLP
T 206.521.3509 E vikram.sami at zgf.com<mailto:vikram.sami at zgf.com>
925 Fourth Avenue, Suite 2400
Seattle, WA 98104
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Baker
Sent: Tuesday, March 03, 2015 7:57 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Modeling air-side economizer
Does equest require a certain HVAC "System Type" before you can add specific air-side economizer inputs?
I'm currently showing "Unit Ventilator" system type in proposed.
Equest won't allow me to add air-side economizer cycle data (dry bulb shutoff, etc...)
Also, would it be reasonable to keep the current systems as-is in equest...
Then add a "sum" system separately to allow ALL zones to receive air-side economizer cooling?
(with sum system on economizer schedule only)
I should also mention that what I'm modeling are the building's pre-existing air handlers with VFD's and no coil attachment.
Our renovation project involved keeping the old AHU's but with on-demand cooling controls.
Chris Baker
CCI CAD Drafter
________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
ZGF Email Disclaimer<https://www.zgf.com/ZGF_Email_Disclaimer.html>
________________________________
CCI-Alliance Confidentiality notice: This message is intended only for the person to whom addressed in the text above and may contain privileged or confidential information. If you are not that person, any use of this message is prohibited. We request that you notify us by reply to this message, and then delete all copies of this message including any contained in your reply. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150304/a7c43135/attachment.htm>
More information about the Equest-users
mailing list