[Equest-users] Excessive summer heating
Singhal, Harshul
HSinghal at ThorntonTomasetti.com
Fri Mar 6 07:31:41 PST 2015
Hi Amy,
The current model (you sent) has 172 unmet load hours coming from zone: "EL5 SSW Perim Zn (G.SSW2)"
I gave a real quick look at model and as per LEED it looks fine to me. DO you mean to decrease these unmet load hours or you already made changes and sent the model here at eQuest group?
I would say check SS-R report and see what zones have unmet load hours & you can increase supply CFM in those particular zones.
Best,
Harshul Singhal, LEED AP BD+C
Project Consultant
Thornton Tomasetti
386 Fore Street, Suite 401
Portland, ME 04101
T +1.207.245.6060 F +1.207.245.6061
D +1.207.245.6074
HSinghal at ThorntonTomasetti.com
www.ThorntonTomasetti.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Harmon, Amy
Sent: Friday, March 06, 2015 9:58 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Excessive summer heating
I received comments back from the LEED reviewers; they comment that I have excessive summer heating. Prior to submitting to USGBC, I had already fooled with the throttling range and system cooling control to warmest. Tweaking those helped with the unmet heating hours I had previously. Could messing with those 2 items before have caused the excessive summer heating? Any suggestions to lower the excessive summer heating? I've attached the inp and pd2 file. I'm running version 3.64.
Any help is appreciated. Thanks!
Amy Harmon
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 107
Direct: (330) 526-2707
Fax: (330) 896-9180
aharmon at sbmce.com<mailto:aharmon at sbmce.com>
www.sbmce.com<http://www.sbmce.com/>
Please consider the environment before printing this email. This e-mail (including any attachments) is confidential and may be legally privileged. If you are not an intended recipient or an authorized representative of an intended recipient, you are prohibited from using, copying or distributing the information in this e-mail or its attachments. If you have received this e-mail in error, please notify the sender immediately by return e-mail and delete all copies of this message and any attachments.
Thank you
<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
The information in this email and any attachments may contain
confidential information that is intended solely for the
attention and use of the named addressee(s). This message or
any part thereof must not be disclosed, copied, distributed
or retained by any person without authorization from the
addressee. If you are not the intended addressee, please
notify the sender immediately, and delete this message.
<><><><><><><><><><><><><><><><><><><><><><><><><><><><><><><>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150306/e7f31843/attachment.htm>
More information about the Equest-users
mailing list