[Equest-users] One Unmet Load Hour Each Day at 3am??
Jones, Christopher
cjones at halsall.com
Wed Mar 11 09:04:17 PDT 2015
If you forward the model pd2 and inp files to the group, you will get an answer fairly quickly.
Christopher Jones, P.Eng.
Tel: 416.644.4226 * Toll Free: 1.888.425.7255 x 527
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Greg Garcia
Sent: Wednesday, March 11, 2015 11:58 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] One Unmet Load Hour Each Day at 3am??
Dear Modeling Friends,
I'm usually good at dealing with Unmet load hours but this one has me stumped.
Issue:
The SS-R shows 365 unmet cooling hours for all spaces in the project. I set up an hourly report on one space to drill into the problem. The hourly output shows "Current Hour Zone Thermostat Setting" dropping down to 34F each day at 3am. When this occurs, the airflow ramps up to max cooling during that hour and cools the space down from 69 to 58F. Then at 4 am, the zone T-stat setting goes back to 69 (in heating) as it should. I've checked my temperature schedules three times and they appear correct. Does anyone have the answer!!:)
Kindly,
Greg Garcia
Engineer, PE
801.278.1927 x111
801.556.0564 (Mobile)
ggarcia at etcgrp.com<mailto:ggarcia at etcgrp.com>
[ETC_Logo_hz_cmyk_lg]
______________________________________________________________________
NOTICE: This communication and any attachments ("this message") may contain confidential information for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on this message is strictly prohibited. If you have received this message in error, or you are not an authorized recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150311/57e215c0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4556 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150311/57e215c0/attachment.jpg>
More information about the Equest-users
mailing list