Here are my two cents:
If you want to obtain valid results that also look good in the 3D drawing, specify outside surfaces to calculate skin loads and scale the inside loads (lights, equipment, infiltration, etc.) to the inner wall dimensions. Specify window setback if they are not at the outside planes of their walls. I do not think that LEED cares about the corner effects, but if you want to get the wall masses correct you can sacrifice the beauty of the 3D drawing by leaving gaps. Just subtract half the thickness of the adjacent corner wall from the actual wall width, leaving the wall to start at the original position, and you get one gap; all you have to change is wall Width. If your wall spans the full building width, you must subtract the two corner wall half thicknesses.
DOE-2 fails to subtract thickness (which is not always specified in the input) from the outer dimensions to calculate internal volumes. Remember that thermal boundaries (building shell) are assumed by DOE-2 to face outward, where the default tilt for walls is 90 degrees, horizontal roofs is zero and floors is 180. Material layers, if user specified, must be entered in the order of outside to inside.
Best regards
for KEMA Services Inc., USA
Glenn Haynes, PE
Senior Engineer, Policy Advisory and Research
DNV GL - Energy
E-mail glenn.haynes at dnvgl.com<mailto:glenn.haynes at dnvgl.com>
DNV KEMA is now DNV GL
Mobile +1 615 856 3557 | Direct +1 615 577 2705
www.dnvgl.com<http://www.dnvgl.com/> | LinkedIn<http://www.linkedin.com/company/dnvgl>
[DNV GL]<http://www.dnvgl.com/>
DNV and GL have merged to form DNV GL
We are now the world's largest ship and offshore classification society, the leading technical advisor to the global oil and gas industry, and a leading expert for the energy value chain including renewables and energy efficiency. We've also taken a position as one of the top three certification bodies in the world. Read more here: www.dnvgl.com/merger<http://www.dnvgl.com/merger>.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton
Sent: Thursday, March 12, 2015 4:17 PM
To: Charudatta Joshi; Singhal, Harshul
Cc: Equest-users
Subject: Re: [Equest-users] Building Geometry
Hi everyone,
I have tread this path a few times before, and my position on the matter has evolved over time. Here’s my current understanding of the issue:
1. Tracing the outside will result in:
a. Inaccurately large interior volumes and
b. Inaccurately large perimeter space areas (pertinent for area-dependent inputs like LPD, plug loads).
2. Tracing the inside will result in:
a. Inaccurately small exterior surface areas for the purposes of determining skin loads.
3. Tracing the middle of the construction results in ALL the inaccuracies above, but to a lesser degree.
I consider the implications between these approaches on your baseline model for Appendix G / LEED / etc. to be arbitrary in nature. Your choice should reflect the degree of accuracy desired relative to the actual/Proposed case and the time you have to invest in your results.
[TIER 1 EFFORT] You could make the case that #1 or #2 is the lesser of two evils, considering the implications (and you might be right either way depending on the circumstances of the project). #3 is a compromise between #1 & #2, and is my first suggestion if you’d rather not get bogged down in such hypotheticals AND need to perform a fast study, acknowledging the above inaccuracies.
[TIER 2 EFFORT] However, a more correct/accurate approach is to put slot yourself into either camp #1 or #2 and then make the necessary corrections in detailed mode (post-wizards) for the known/stated inaccuracies with that approach.
Of the two, I personally think #1: tracing the outside and making corrections for space volume and lighting/rcpt inputs, is the more intuitive approach and has the (subjective) advantage of a model that will look correct in 3D view. Others will trend towards the second approach, and I wouldn’t fault them for it.
[TIER 3 EFFORT – HERE BE DRAGONS!]
This isn’t really part of the original “black/white” question, but it seems worthwhile to insert a heads up:
To first speak to what’s happening “under the hood,” I believe it’s most correct to say eQUEST/DOE2 doesn’t actually “simulate” the thickness of a construction (i.e. “outward-in” vs. “inward-out”), rather the construction and heat transfer is 1-dimensional. (I swear, this is rather pertinent for a thick-wall study – bear with me!) While we DO enter thickness of materials/layers for exterior constructions in eQUEST, those inputs are used only to determine the construction’s thermal mass and conductivity. This means each hour of the simulation, heat is determined to be moving either in or out, perpendicular to the surface. Heat is not simulated to move “sideways” within the construction (as actually happens at building corners and where materials change along/within the assembly, such as with stud wall assemblies) – that would be what people are referring to when they speak of 2-dimensional heat transfer. Usually, we make efforts to define our construction layers in uniform terms (i.e. for a stud/insulation layer), and call it a day.
So what does all this mean for a thick wall study? (Consider how heat would travel through the cross-section of a vertical building corner…) It means the “effective” 1-dimensional exterior surface area for a space with skin loads actually lies somewhere between options #1 and #2, above. A “most correct” eQUEST model might most closely resemble approach #3, above.
I will insert here: I have done some homework in the way of self-educating to read up on the topic & attend related seminars, and I even passed a thermodynamics course back in college, but I do not presently consider myself an expert on multi-dimensional heat transfer in building assemblies, and haven’t had a ton of experience putting this to practice. I do know others on this list are more solidly situated in those camps and are welcome/encouraged to fill in gaps & participate!
So take approach #3 as a framework: To arrive at a “most-correct” study using eQUEST (and it may be prudent at this stage to instead consider software with 2D/3D heat transfer baked-in): Rather than arbitrarily define walls along the centerlines of your envelope, I would propose estimating at what mean construction thickness (between the interior and exterior thicknesses) you would achieve the same result in 1-dimensional transfer as you would with a more sophisticated 2D (or even 3D) analysis. You would still need to later make corrections for interior volume and space-dependent internal loads, as suggested under approach #1.
Procedurally, I would not be surprised to learn others have come up with tools or a rule of thumb to estimate such an “effective 1-dimensional thickness,” accounting for the surface perimeter:area ratio in addition to the usual conductive variables. You might also use a separate study/software to externally determine what this effective thickness should be. Again, I haven’t tread this path in practice, and am hopeful others may chime in with suggestions along these lines.
I hope this was illuminating/helpful to some (even if only to help you fall asleep!),
~Nick
NICK CATON, P.E.
Owner
Caton Energy Consulting
1150 N. 192nd St., #4-202
Shoreline, WA 98133
office: 785.410.3317
www.catonenergy.com
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Charudatta Joshi
Sent: Thursday, March 12, 2015 1:21 PM
To: Singhal, Harshul
Cc: Equest-users
Subject: Re: [Equest-users] Building Geometry
Inside edge is better in your case. Just make sure you model exterior constructions using the layers input, so you account for thermal mass.
(Larger projects can be modeled with outside edge of walls so your modeled area matches what's declared as total building area in the architectural drawings, or in other LEED credits, as applicable).
CJ
On Mar 12, 2015 1:05 PM, "Singhal, Harshul" <HSinghal at thorntontomasetti.com<mailto:HSinghal at thorntontomasetti.com>> wrote:
Hi Maria,
We have done one university block recently which had 2.5 feet thick walls (retrofit) and we modeled using inner dimensions. Whether it’s thick or thin, its advised to use inner dimensions although project requirements vary sometimes. Thanks!
Harshul Singhal, LEED AP BD+C
Project Consultant
Thornton Tomasetti
386 Fore Street, Suite 401
Portland, ME 04101
T +1.207.245.6060<tel:%2B1.207.245.6060> F +1.207.245.6061<tel:%2B1.207.245.6061>
D +1.207.245.6074<tel:%2B1.207.245.6074>
HSinghal at ThorntonTomasetti.com<mailto:HSinghal at ThorntonTomasetti.com>
www.ThorntonTomasetti.com<http://www.ThorntonTomasetti.com>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Maria Elisa Rumeo
Sent: Thursday, March 12, 2015 2:51 PM
To: Farid Pour
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Building Geometry
Does anyone have experience with modelling thick-wall retrofits who can also answer my question?
It is a small house, so if I trace the interior dimensions I will get significantly different results than tracing exterior dimensions
On Thu, Mar 12, 2015 at 2:11 PM, Farid Pour <farid.pour at hok.com<mailto:farid.pour at hok.com>> wrote:
As far as I know, it goes in.
From: Maria Elisa Rumeo [mailto:rumeomar at gmail.com<mailto:rumeomar at gmail.com>]
Sent: Thursday, March 12, 2015 1:10 PM
To: Farid Pour
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Building Geometry
Hello,
It is a low-energy retrofit and the walls are really thick!
My fear is that by using the outside dimensions, then if the wall contruction goes 'outward' of these defined lines, then I am modelling a larger house ( the volume of the house in the model is greater than the actual volume) .
please help :)!
thanks,
maria
On Thu, Mar 12, 2015 at 2:05 PM, Farid Pour <farid.pour at hok.com<mailto:farid.pour at hok.com>> wrote:
It should not make that much of difference unless your walls are rally thick. I suggest you trace the outside wall and then make sure of the wall thermal properties.
Farid
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Maria Elisa Rumeo
Sent: Thursday, March 12, 2015 1:03 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Building Geometry
Hello,
Can someone please help me with this:
I have an AutoCAD file of an old home that was retrofitted with thick (insulated walls). When I import this file and trace it to define the building footprint on eQuest,should I be tracing the OUTSIDE of the building (the brick face) or the INTERIOR of the building (the interior walls)? or should I draw a line in the middle of them and use that as my building footprint?
do you know the wall construction goes INWARD or OUTWARD from the building footprint you set?
thanks,
maria
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
**************************************************************************************
This e-mail and any attachments thereto may contain confidential information and/or information protected by intellectual property rights for the exclusive attention of the intended addressees named above. If you have received this transmission in error, please immediately notify the sender by return e-mail and delete this message and its attachments. Unauthorized use, copying or further full or partial distribution of this e-mail or its contents is prohibited.
**************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150313/6156716e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 2815 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150313/6156716e/attachment.gif>
More information about the Equest-users
mailing list