[Equest-users] eQuest & NoteTab Question
Jones, Christopher
Christopher.r.Jones at wspgroup.com
Fri Sep 11 06:09:46 PDT 2015
I use UltraEdit for editing .inp files. After doing the search and replace PSZ for HP, I recorded a macro that first searches for ‘PSZ’, then searches for ‘ = ZONE’. Then
[cid:image003.png at 01D09C46.E75BA0D0]
Christopher Jones, P.Eng.
Senior Engineer
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
T +1 416-644-4226
F +1 416-487-9766
C +1 416-697-0065
www.wspgroup.com<http://www.wspgroup.com/>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Reddy
Sent: Thursday, September 10, 2015 11:56 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest & NoteTab Question
We typically use RegExs for tasks like this as well, but I had not run across the Regular Expressions 101<https://regex101.com/> site before; what a great resource Julien! Very cool way to keep track of expressions and share. Thanks for circulating these examples!
David
On 9/10/2015 12:26 AM, Julien Marrec wrote:
Jesse,
I've created an example here : https://regex101.com/r/iZ5jO8/1. This should really help understanding how I'm getting the result, by decomposing each step of the regex.
Note that I added names to capturing groups, you don't have to do that, you could use just positional:
Look for: (SYSTEM *\n *?TYPE *= )HP(.*?FURNACE-HIR +?= [.0-9]+)\n(.*?\.\.\n)(\".*?\")
Replace with: \1PSZ\2\n CONTROL-ZONE = \4\n\3\4
A few things: dot (.) has to match newline characters for it to work.
Also, in notepad++ to replace with named capturing groups, you use $+{Name}
You have to replace \n (unix convention) by \r\n.
Anyways, for notepad++ try:
Search:
(?<System1>SYSTEM *\r\n *?TYPE *= )HP(?<System2>.*?FURNACE-HIR +?= [.0-9]+)\r\n(?<System3>.*?\.\.\r
\n)(?<ZoneName>\".*?\")
Replace with:
$+{System1}PSZ$+{System2}\n CONTROL-ZONE = $+{ZoneName}\n$+{System3}$+{ZoneName}
I've loaded it up in eQuest, seems to do the job just fine. Let me know if you are trouble implementing. I've also attached the file back, but I'd be a shame to not take this as an opportunity to learn regex
PS: By the way, you should really use floor multipliers.
Best,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13
LinkedIn (en) : www.linkedin.com/in/julienmarrec<http://www.linkedin.com/in/julienmarrec>
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr<http://www.linkedin.com/in/julienmarrec/fr>
2015-09-09 22:32 GMT+02:00 Phillips, Jesse <jphillips at rdkengineers.com<mailto:jphillips at rdkengineers.com>>:
Thanks Julien.
I’ve attached the inp file. I am not familiar with Regex at all but I’ll check out that website. If you could send me some examples tomorrow though, that would be great!
thanks,
Jesse
From: Julien Marrec [mailto:julien.marrec at gmail.com<mailto:julien.marrec at gmail.com>]
Sent: Wednesday, September 09, 2015 4:27 PM
To: Phillips, Jesse <jphillips at RDKEngineers.com><mailto:jphillips at RDKEngineers.com>
Cc: Nathan Miller <nathanm at rushingco.com<mailto:nathanm at rushingco.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] eQuest & NoteTab Question
Hi,
I don't know Notetab, but as long as you have one system for each zone, this is pretty easy if your editor supports Regular Expressions (Regex).
As you might know, inp files has what I call a positional input for a few things (space > surface > window/door, same for system > zone). Meaning if you find something that is a system, everything that's right after (which are zones) below to this system until you find another system. As opposed to having a keyword linking those two objects.
So you could use a regex for this job. Especially using positive lookaheads to delimit a single system and its zone (singular here, could be plural).
If you do have only a single zone per system, it's even easier.
Just look for a system and it's zone below it.
If you are not familiar with regex and can't manage to build it, let me know, I'll try to find a few tomorrow to help you out (send me your file or an extract or it so I don't have to create a dummy one to play with it).
By the way, here's a website I wish existed when I first started playing with regex: https://regex101.com/. Fyi, Notepad++ uses the prce engine.
Cheers,
Julien
--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13<tel:%2B33%206%2095%2014%2042%2013>
LinkedIn (en) : www.linkedin.com/in/julienmarrec<http://www.linkedin.com/in/julienmarrec>
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr<http://www.linkedin.com/in/julienmarrec/fr>
2015-09-09 22:04 GMT+02:00 Phillips, Jesse <jphillips at rdkengineers.com<mailto:jphillips at rdkengineers.com>>:
I don’t think you can create macros in NoteTab. What would that macro look like in boxer?
Jesse Phillips
Energy Engineer
RDK Engineers
P: 857-221-5957
From: Nathan Miller [mailto:nathanm at rushingco.com<mailto:nathanm at rushingco.com>]
Sent: Wednesday, September 09, 2015 3:38 PM
To: Phillips, Jesse <jphillips at RDKEngineers.com<mailto:jphillips at RDKEngineers.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: eQuest & NoteTab Question
Can you create a macro that searches for each instance of “=ZONE”, copies the text before the “=” to get the zone name, and the pastes in the lines necessary to create a new single zone system, using the zone name now stored in the clip-board to paste in the control zone?
I’m not familiar with NoteTab, but you can do that in boxer.
Nathan Miller, PE, LEED AP BD+C – Mechanical Engineer/Senior Energy Analyst
RUSHING | D 206-788-4577 |O 206-285-7100
www.rushingco.com<http://www.rushingco.com>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Phillips, Jesse
Sent: Wednesday, September 09, 2015 3:23 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQuest & NoteTab Question
Hi,
I have a model with 233 zones. Right now, every zone has a water loop heat pump. I want to convert these all to packaged single zone systems. To do this, I am working in the .inp file and doing a “find and replace” in NoteTab. The replacing of the system type is easy. I simply search for the “type = HP” line and replace with “type = PSZ”. However, the PSZ system requires a control zone. I would like each control zone to be the zone in which that particular system resides. Which means, for each of my 233 zones, I will have a different control zone (i.e. no longer a simple find and replace search).
Does anyone know of a way to use “find and replace” (or another method) to set each control zone with the zone name which the system resides?
This is what the .inp file should look like for a packaged single zone system:
"EL1 Sys1 (PTAC) (G.SSW1)" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HEAT-PUMP
ZONE-HEAT-SOURCE = NONE
SIZING-RATIO = 1
COOL-SIZING-RATI = 1
MIN-SUPPLY-T = 58
FAN-SCHEDULE = "S1 Sys1 (PTAC) Fan Sch"
CW-LOOP = "DEFAULT-CW"
COOLING-CAPACITY = 15752
COOL-SH-CAP = 11839
HP-SUPP-SOURCE = NONE
FURNACE-HIR = 1.24067
CONTROL-ZONE = "EL1 SSW Perim Zn (G.SSW1)"
C-EER95 = 8.24
C-COP47 = 0.78
C-AFUE = 0.78
C-SF-MTR-TYPE = 1
C-RF-MTR-TYPE = 1
C-OSA-DMPR-CTRL = 1
C-HTG-DUCT-LOCN = *Ceiling Plenum*
C-HTG-DUCT-RVAL = 7
C-CLG-DUCT-LOCN = *Ceiling Plenum*
C-CLG-DUCT-RVAL = 7
C-CLG-CAP-CATEG = 14
For my next system, everything would be exactly the same except the highlighted lines (and so on for all 233 systems):
"EL1 Sys1 (PTAC) (G.W2)" = SYSTEM
TYPE = PSZ
HEAT-SOURCE = HEAT-PUMP
ZONE-HEAT-SOURCE = NONE
SIZING-RATIO = 1
COOL-SIZING-RATI = 1
MIN-SUPPLY-T = 58
FAN-SCHEDULE = "S1 Sys1 (PTAC) Fan Sch"
CW-LOOP = "DEFAULT-CW"
COOLING-CAPACITY = 15752
COOL-SH-CAP = 11839
HP-SUPP-SOURCE = NONE
FURNACE-HIR = 1.24067
CONTROL-ZONE = "EL1 Sys1 (PTAC) (G.W2)"
C-EER95 = 8.24
C-COP47 = 0.78
C-AFUE = 0.78
C-SF-MTR-TYPE = 1
C-RF-MTR-TYPE = 1
C-OSA-DMPR-CTRL = 1
C-HTG-DUCT-LOCN = *Ceiling Plenum*
C-HTG-DUCT-RVAL = 7
C-CLG-DUCT-LOCN = *Ceiling Plenum*
C-CLG-DUCT-RVAL = 7
C-CLG-CAP-CATEG = 14
thank you,
Jesse Phillips | Energy Engineer
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
________________________________
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance at wspgroup.com<mailto:caslcompliance at wspgroup.com> so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received.
WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150911/9752c90f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6574 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20150911/9752c90f/attachment.png>
More information about the Equest-users
mailing list