[Hap-users] Boiler Hot Water Reset
    Reba Schaber 
    Rschaber at PHMECH.com
       
    Tue Aug 16 10:46:05 PDT 2011
    
    
  
Jason,
I just had this issue.  GBCI has not reviewed it yet, but my strategy was to average the two conditions.  180 with 130 degree return is a 50 degree delta-T.  150 with 130 degree is a 20 degree delta-T.  I ran the simulation once with the boiler and plant at a 50 degree delta-T and ran it a second time with a 20 degree delta-T.  Then I used the average values of the two runs.  I left the system delta-T at 50 for both runs.  The system delta-T did not seen to effect the simulation results.
A better approximation might be a weighted average using the ambient dry bulb in the TMY data to figure how many hours would be spent at each delta-T.  Of course you'd want to exclude the hours when the system is not scheduled to operate.
When I emailed Carrier HAP support they said, "We cannot currently model Hot Water reset of boiler temperature in HAP 4.51. For purposes of LEED, you must write a narrative explaining that the program you are using for LEED does not have this capability.
We do have Supply Air Temp reset on a hot water coil in an air system.
Hot Water Boiler reset is on our list for a future version of HAP."
Good luck.
         Reba Schaber      Mechanical Engineer, P.E.
                                     LEED Accredited Professional
From: hap-users-bounces at lists.onebuilding.org [mailto:hap-users-bounces at lists.onebuilding.org] On Behalf Of Jason D. Plumpton
Sent: Monday, July 25, 2011 12:54 PM
To: hap-users at onebuilding.org
Subject: [Hap-users] Boiler Hot Water Reset
Hello,
Has anyone had any luck modeling HW reset in HAP 4.51?
90.1-2007 Appendix G calls for this type of control in G3.1.3.4, and I am assuming that there must be some way of modeling this reset control in HAP.
Any advice/help would be greatly appreciated.
Thank You,
Jason D Plumpton, P.E. LEED-AP
M/E Engineering, P.C.
________________________________________________________________________
This Email has been scanned for all viruses by PAETEC's Hosted E-mail Security Services, utilizing MessageLabs proprietary SkyScan infrastructure. For more information on a proactive anti-virus service working around the clock, around the globe, visit http://www.paetec.com.
________________________________________________________________________
________________________________
No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 10.0.1390 / Virus Database: 1518/3787 - Release Date: 07/25/11
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachments/20110816/5189d817/attachment.htm>
    
    
More information about the Hap-users
mailing list