[Hap-users] Hap-users Digest, Vol 53, Issue 3
Aaron Smith
asmith at mreng.ca
Sun Dec 14 19:27:36 PST 2014
Danny,
I'd recommend contacting Carrier software support - I find them to be pretty
helpful.
That being said, I don't think HAP can model wrap-around coils and it can't
model outdoor air from another system. Here are my suggestions but they may
not be of much help:
As a work-around to allow you to model the rooftop AHU conditioning outdoor
air, you could model the floor level AHUs without any outdoor air (in each
space, select OA ventilation requirements as "user defined" then enter "0").
Then model a separate AHU with all of the building's outdoor air (you'll
need to create a dummy space for it and enter all of the building's outdoor
airflow into this space). This may work ok if you are supplying neutral
temperature outdoor air to the floors but if not; you'll probably want to
incorporate the rooftop AHU fan power and coil capacities into the floor
AHUs.
As for the free reheat you are getting from the wrap around coil, I see that
v4.9 has a heat recovery chiller - that may be the best way to simulate it.
I haven't installed v4.9 yet so I'm not familiar with how that works but I
don't think you would want to have that chiller serve the floor level AHUs
as it would make too much free heat recovery available to the whole building
- you probably only want to use this if you choose to model a separate
rooftop AHU as you could have your heat recovery chiller only serve that
AHU.
Aaron
Aaron Smith, P.Eng
M&R Engineering
-----Original Message-----
From: Hap-users [mailto:hap-users-bounces at lists.onebuilding.org] On Behalf
Of hap-users-request at lists.onebuilding.org
Sent: Sunday, December 14, 2014 6:39 PM
To: hap-users at lists.onebuilding.org
Subject: Hap-users Digest, Vol 53, Issue 3
Send Hap-users mailing list submissions to
hap-users at lists.onebuilding.org
To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/hap-users-onebuilding.org
or, via email, send a message with subject or body 'help' to
hap-users-request at lists.onebuilding.org
You can reach the person managing the list at
hap-users-owner at lists.onebuilding.org
When replying, please edit your Subject line so it is more specific
than "Re: Contents of Hap-users digest..."
Today's Topics:
1. Modeling Pre-cooled Ventilation Air (Daniel Lim)
----------------------------------------------------------------------
Message: 1
Date: Sun, 14 Dec 2014 14:41:52 +0000 (UTC)
From: Daniel Lim <dannyllim at yahoo.com>
To: "hap-users at lists.onebuilding.org"
<hap-users at lists.onebuilding.org>
Subject: [Hap-users] Modeling Pre-cooled Ventilation Air
Message-ID:
<1464281635.275591.1418568112617.JavaMail.yahoo at jws10045.mail.ne1.yahoo.com>
Content-Type: text/plain; charset="utf-8"
I am new to HAP and would appreciate advice or guidance from the HAP-user
forum. I am modeling floor level AHUs receiving pre-cooled fresh air from
rooftop pre-cooling AHU equipped with wrap around??heat pipe (AHU cooling
coil between heat pipe cooling section and heating section) to remove
moisture. I am using HAP 4.9 and the closest I can find to start with is the
CAV Tempering Ventilation system but can't figure out how to make it feed
the floor level AHUs. Can this configuration be implemented in HAP? Thanks
in advance for any guidance.
Danny Lim??
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.onebuilding.org/pipermail/hap-users-onebuilding.org/attachment
s/20141214/d9c10381/attachment.html>
------------------------------
Subject: Digest Footer
_______________________________________________
Hap-users mailing list
Hap-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/hap-users-onebuilding.org
------------------------------
End of Hap-users Digest, Vol 53, Issue 3
****************************************
More information about the Hap-users
mailing list