[Hap-users] How to added treated cooled fresh air
Michael Hardy
mhardy at blackoakengineering.com
Thu Oct 9 08:54:25 PDT 2014
HAP only allows one system per space, so your choices are to either 1.) select a system that incorporates all of the components, 2.) split a room into multiple spaces and assign different systems to each space or 3.) use the system sizing results from HAP as inputs to design your own equipment using a spreadsheet or other engineering tools. Experience and your best engineering judgment needs to be applied with all of these options.
If System #1 “cooling fresh air” is providing the majority of the cooling and System #2 “fan coil unit” is providing heating only, then you would select the appropriate system type for System #1 and then add the Fan Coils under the “Zone Components: Zone Heating Units” tab of the Systems screen.
If System #1 “cooling fresh air” is only providing tempered ventilation air, then you should probably select “Terminal Units” as your system type and then “Common Ventilation Unit” (see Help 30.0 Terminal Unit Systems”
I hope this helps.
Michael L. Hardy, PE, F.NSPE
Black Oak Engineering, Inc.
Cell 503.314.5244
From: Hap-users [mailto:hap-users-bounces at lists.onebuilding.org] On Behalf Of az_zahran
Sent: Thursday, October 09, 2014 4:44 AM
To: hap-users at lists.onebuilding.org
Subject: [Hap-users] How to added treated cooled fresh air
I had been tried to added the cooled fresh air to the zones with out Dublicate the cooling load .as I have two system
1 - cooling fresh air for zone
2- fan coil unit for each for space
Thanks&Best Regards
Sent from my Samsung Galaxy smartphone.