[Trace-users] Appendix G Fan Energy
Jeremy Poling
jpoling at epsteinglobal.com
Thu Oct 29 08:14:17 PDT 2009
Marty,
The equations in Section G3.1.2.9 and Table G3.1.2.9 are only for the
baseline building. For the baseline building, the supply CFM is used to
model the efficiency of all of the fans in the building based on
assumptions about minimum design characteristics. If you are using the
equations, you should use the Supply CFM for the system, run through the
equations in Table G3.1.2.9 to determine the BHP for the baseline, then
run that through the equation in G3.1.2.9 to determine total fan power
in kW. That value can then be input into Trace for fan power.
For the proposed building, you should use the actual rated fan kW based
on the fan power curve for your CFM and the fans specified.
As Bob stated, Trace does have an option where it will do the
conversions for the baseline building, but I typically have not used it.
I shy away from the "black boxes" in energy modeling when putting things
together for a LEED review team since ANYTHING is up for grabs when they
review the credit and if I can't explain a black box process they may
deny the entire credit.
JEREMY R. POLING, PE, LEED AP
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Architecture
Interiors
Engineering
Construction
600 West Fulton Street
Chicago, Illinois 60661-1259
D: (312) 429-8152
F: (312) 559-1217
C: (312) 504-5905
E: jpoling at epsteinglobal.com <mailto:jpoling at epsteinglobal.com>
W: www.epsteinglobal.com <http://www.epsteinglobal.com/>
Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.
________________________________
From: trace-users-bounces at lists.onebuilding.org
[mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Snarski,
Marty
Sent: Tuesday, October 27, 2009 1:33 PM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] Appendix G Fan Energy
Hello, all.
I'm running an energy model (for LEED), and am having a particular
problem with the Fan Energy results. I am using the actual fan
horsepower (for the supply and for the return fans) for the proposed
building, and the Appendix G equation in G3.1.2.9. The results I'm
getting for the proposed design are considerably higher (about 31%) than
the baseline building. This leads me to believe that I may be
misinterpreting the equation.
As stated in the 90.1 Users manual, the equation accounts for supply,
return, relief, and exhaust fans. However, I've been simply inputting
the Supply CFM into the equation. Given that it accounts for all fans,
should I use the accumulated CFMs for each of those fans (i.e. if I'm
supplying 32,000, and returning 24,000, should I use 56,000 cfm)?
While I understand TRACE has the automatic baseline fan sizing
capability, I'm not sure I trust it completely, and would like to know
where the calculation comes from.
Thanks for any help you can offer!
NOTICE:
This e-mail transmission is intended only for the use of the individual
or entity named above and may contain information that is confidential,
privileged, and/or exempt from disclosure under applicable law. If you
are not the intended recipient, you are hereby notified that any review,
disclosure, copying, distribution, or other use of any of the
information contained in this transmission is strictly prohibited. If
you have received this transmission in error, please immediately notify
the sender by e-mail at the above address and delete it from your
computer system; you should not copy the message or disclose its
contents to anyone. The content of the message and or attachments may
not reflect the view and opinions of the originating company or any
party it is representing.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20091029/1d9b4865/attachment-0002.htm>
More information about the Trace-users
mailing list