[Trace-users] how to model Hotgas Bypass in Trace700

Duncan S. McClellan dmcclellan at ClarkNexsen.com
Thu Aug 29 07:41:08 PDT 2013


I would create a flat-line performance curve that consumes 100% energy consumption at all load conditions.  I would not run flat line all the way to 0% load however.  Determine what your minimum running capacity is and drop it off to 0 at that point.  The example below could be used for HGBP with a min. capacity at 5%.  I'm not sure what's the typical minimum.

[cid:image003.png at 01CEA4A4.44A7EA10]


Duncan McClellan PE, BEMP, LEED AP
Mechanical Engineer

CLARK NEXSEN
Architecture & Engineering
6160 Kempsville Circle Suite 200A
Norfolk, VA 23502
757.455.5800 Office
757.455.5638 Fax
dmcclellan at clarknexsen.com<mailto:dmcclellan at clarknexsen.com>
www.clarknexsen.com<http://www.clarknexsen.com%20>
From: trace-users-bounces at lists.onebuilding.org [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Caballero, Catalina
Sent: Thursday, August 29, 2013 8:55 AM
To: trace-users at lists.onebuilding.org
Subject: [Trace-users] how to model Hotgas Bypass in Trace700

Hello experts.

I was wondering how can I model hotgas bypass in Trace700?

Thanks

Catalina Caballero, AIA. Assoc., LEED GA.
Johnson, Avedano, Lopez, Rodriguez & Walewski
Engineering Group, Inc.

2510 NW 97th Avenue, Suite 220, Miami, Florida 33172
Tel. (305) 594-0660 Ext. 217 Fax (305) 594-0907

Visit us online: www.jalrw.com<http://www.jalrw.com/>

[JALRW Logo]          [member_blk]

HVAC - Electrical - Plumbing - Fire Protection
Sustainable Development - Commissioning


This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to which they are addressed. If you are not the intended recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited.





----------------------------------------------------------------------

Clark Nexsen Email Security: Click here<https://www.mailcontrol.com/sr/S63Tk4tG9yDGX2PQPOmvUkWM85sEKD4+botdix5KH8UD4zb2v4veXWDa0MC7WsimBtgi9HH78G1jDxGYc2QXWA==> to report this email as spam.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130829/4b267a2c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4129 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130829/4b267a2c/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 3230 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130829/4b267a2c/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 56516 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20130829/4b267a2c/attachment-0005.png>


More information about the Trace-users mailing list