[TRNSYS-users] TESS Chiller Models
Jeff Thornton
thornton at tess-inc.com
Wed Aug 1 08:45:41 PDT 2012
The chiller performance data files were created from published
catalog data from manufacturer's web sites. In some cases the data files
represent a single manufacturer/size and in other cases they represent
an average across a range of manufacturers and sizes - it depends on the
data file that you have chosen. A "rating condition" is chosen and then
all other data points are then normalized to the capacity and power at
the rating condition. That's why the capacity and power consumption
supplied to the proforma model should correspond to the condition in the
data file where the normalized ratios are 1. Besides the simple set
supplied with the TESS Library install, we have dozens of other data
files if you're looking for something in particular.
Jeff
---
Jeff
Thornton
_President - TESS LLC_
_22 N. Carroll Street, Madison WI
USA 53703_
_Office: (608) 274-2577 Fax: (608) 278-1475_
_www.tess-inc.com_
_E-Mail: thornton at tess-inc.com_
On 07/31/2012
6:17 pm, Santiago Naranjo Palacio wrote:
> Dear TRNSYS-users,
>
> I
have been using both of the chiller models supplied by TESS (Type 655
and 666) and I have a couple of questions regarding the data files
needed to use them. How were exactly these numbers obtained (the
Capacity Ratio and COP ratio)? I am trying to use the chillers for
different chilled water temperature settings and ambient temperatures
and I was wondering how to do this. If I understand the model correctly,
this means that these chillers only approximate power consumption based
on the data provided and there is no other criteria. Correct?
>
> I
would greatly appreciate any input.
>
> Thanks
>
> --
> Santiago
Naranjo Palacio, Ph.D. Candidate
> Cornell University, New York
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120801/1b813a00/attachment-0001.htm>
More information about the TRNSYS-users
mailing list