[TRNSYS-users] how to set simulation START ant Timestep to avoid error
David BRADLEY
d.bradley at tess-inc.com
Wed Aug 22 10:15:29 PDT 2012
Karol,
We are working on a solution. The error seems to be dependent on what
computer the simulation is being run on and on what compiler we use to
create the DLL. For the time being, the workaround seems to be to use a
timestep that conforms to 1/(2**n) where n is an integer. Please try
using a timestep of 0.125 and let me know if that works. We will get a
patch released as soon as possible with an actual fix.
Regards,
David
On 8/22/2012 07:54, Karol Bandurski wrote:
>
> Dear all
>
> I would like to change 'Simulation start time' from 0 to eg. 2880 hr,
> my time step is 10 min -- attached PICTURE_1
>
> The problem is that when I set it, I get error from Type 15:
>
> 'Unable to correctly read from the supplied data file - please check
> the file and re-run the simulation.'
>
> I found response of Matt Duffy related to this issue:
>
> https://mailman.cae.wisc.edu/pipermail/trnsys-users/2011/007369.html
>
> but I don't understand it.. I have changed my setting as you can see
> on attached PICTURE_2 and error occurs again.
>
> Could you help me?
>
> Regards,
>
> Karol
>
> ------------------------------------------------
>
> Karol Bandurski MSc.
>
> Institute of Environmental Engineering <http://www.ee.put.poznan.pl/>
>
> Poznan University of Technology
>
> www.ee.put.poznan.pl <http://www.ee.put.poznan.pl/>
>
> www.put.poznan.pl <http://www.put.poznan.pl/>
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20120822/5413d3e1/attachment-0001.htm>
More information about the TRNSYS-users
mailing list