Florian,
That is a really bad message coming from Type556! I notice in the
list file that there are a lot of notices that the water temperatures
being passed to (or calculated by) the Type177 chiller are out of the
range for that model. I am not familiar with Type177 so I can't offer
much comment about it but what I would recommend is that you remove the
Type556 from the simulation and run it again watching the outlet
temperatures from Type177 so as to make sure that the model is not
passing junk to Type556. If that doesn't help then you may forward the
project and the code for Type177 to me as I would like to try and see if
I can find out why the error message in 556 is junk. This being a
Trnsys16 project, I can't promise that I will be able to do much about
it even if I am able to find the problem in 556.
Kind regards,
David
On 3/14/2013 14:15, Florian Weiß wrote:
> Dear TRNSYS-community
> i added my list-file from my last try to implement a buried pipe
> ground heat exchanger into an existing system by removing a solar
> collector.
> In the list-file is a discribtion on a Unkown message from Type 556
> which transformed to a Fatal Error and interrupts the running simulation.
> Anyone an idea?
> Thank you in advance.
> Florian
> student of the technical university of Berlin
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130314/e06f9c35/attachment-0001.htm>
More information about the TRNSYS-users
mailing list