[TRNSYS-users] Boundary wall and Qcomo
David BRADLEY
d.bradley at tess-inc.com
Thu Mar 28 11:01:12 PDT 2013
Jingyu,
Setting the back side convection coefficient to a small but non-zero
number indicates direct contact with a known (or calculated)
temperature. It does not mean that there is no energy transferred
through the surface. If you want to create an adiabatic surface within
the wall you can set the convective coefficient to zero. QCOMO is the
energy transferred through the outside surface of the wall. So long as
the wall temperature and the boundary temperature are different, there
will still be some energy transferred.
Kind regards,
David
On 3/22/2013 22:27, 璟瑜 黄 wrote:
> Dear user:
> I have created a boundary wall whose temperature is provided by
> myself. And I have set the coefficient of convective heat transfer of
> back side to 1e-006 and solar absorptance of back side to 0. I suppose
> the Qcomo will be 0 but it is thousands. Why? Qcomo is consisted by
> convective and radiation, isn't it?
> Jingyu Huang
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20130328/08313d5b/attachment-0001.htm>
More information about the TRNSYS-users
mailing list