[TRNSYS-users] solar collector drainback
Jeff Thornton
thornton at tess-inc.com
Mon Nov 4 09:17:27 PST 2013
We have been modeling solar hot water systems for years and we never
model the physical draining of the solar collector and pipes. We include
a drainback tank for the additional losses that it provides and set up
controls to mimic the operation of a drainback system. We allow the pump
to run a bit longer after it turns off in order to fill the drainback
tank (variable volume tank Type 39) with fluid to it's "drainback
volume". At start-up of the pump, we "throw away" the fluid returning
from the collector and return line using a diverting valve until the
drainback tank reaches it's "operating volume". While this isn't
perfect, developing pipe and collector models that deal with both air
and water filled sections would be difficult. Besides, the amount of
energy that we are talking about is usually very small when compared to
the total amount of collected energy over the year.
Jeff
---
Jeff
Thornton
_President - TESS LLC_
_22 N. Carroll Street, Madison WI
USA 53703_
_Office: (608) 274-2577 Fax: (608) 278-1475_
_www.tess-inc.com_
_E-Mail: thornton at tess-inc.com_
On 11/04/2013
9:11 am, Pascual Ortiz, Carol wrote:
> Dear all,
>
> I would also
like to simulate the drain-back of a flat plate collector but I do not
know how to do it. So far, I simulated the FPC using the type 1b but now
I do not know how can I simulate the drain-back, because if the inlet
flow rate of the collector is zero kg/h also the outlet flow rate will
be zero. I think that I should change the type 1 for another one, but I
do not know which is the type that I should use, could you give me a
clue, please?
>
> Thank you in advance,
>
> CAROL PASCUAL
>
>
Energía Térmica/Thermal Energy
>
> DIVISIN DE ENERGA Y MEDIO AMBIENTE/
>
> ENERGY AND ENVIRONMENT DIVISION
>
> TECNALIA
>
> Área Anardi,5
>
> Laida Bidea, Edificio 204
>
> E-20730 Azpeitia - Gipuzkoa
(Spain)
>
> T 902 760 000*
>
> M 667119581
>
> T +34 946 430 850
(International calls)
>
> carol.pascual at tecnalia.com [1]
>
>
www.tecnalia.com [2]
>
> [3]
>
> Este mensaje puede contener
información confidencial o privilegiada. Si no eres el destinatario de
este mensaje, notifícaselo por favor al remitente y bórralo sin
reenviarlo o guardarlo dado que está legalmente prohibido.
>
> Mezu
honek daukan informazioa isilpekoa edo pribilegiatua izan daiteke. Zuri
zuzendua ez badago emaiozu, mesedez, horren berri igorleari eta ezaba
ezazu bidali edo gorde gabe, legalki debekatua dago eta.
>
> This
message may contain confidential, proprietary or legally privileged
information. If you are not the intended recipient of this message,
please notify it to the sender and delete without resending or backing
it, as it is legally prohibited.
>
> Por favor, piensa en el medio
ambiente antes de imprimir este e-mail.
>
> Mesedez pentsatu
ingurugiroan e-mail hau imprimatu baino lehen.
>
> Please, consider
the environment before printing this e-mail.
Links:
------
[1]
mailto:carol.pascual at tecnalia.com
[2] http://www.tecnalia.com/
[3]
http://www.tecnalia.com/pulseraverde/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131104/143789df/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 5959 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131104/143789df/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 37178 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131104/143789df/attachment-0001.jpg>
More information about the TRNSYS-users
mailing list