[TRNSYS-users] how to set three input temperatures in a single building type
David BRADLEY
d.bradley at tess-inc.com
Thu Nov 21 07:11:16 PST 2013
Qi,
As I said in my email to you a few days ago, you can define multiple
groups of zones in Type56 that have nothing to do with each other
thermally. So while it is true that you can only have one instance of
Type56 in your simulation, that Type56 can be used to simulate how ever
many separate buildings (or parts of buildings) that you want.
As far as defining more than one soil temperature, you simply need to
define new ground temperature inputs for the BOUNDARY temperature in
each section of the building. Defining non-standard inputs to Type56 is
an important, basic operation when working with this model. It would be
wise, I think, to study a few of the examples that use Type56 and to
look carefully through the 05-MultizoneBuilding manual (particularly the
first part that focuses on the use of TRNBuild). You may also benefit
from going through the "temperature level control from energy rate
control" tutorial that is available from
http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm.
While the tutorial does not directly deal with setting boundary
temperatures, it does show how to manage Type56's inputs and outputs;
something you will need to do as well.
Regards,
David
On 11/21/2013 06:10, Cheng Qi wrote:
> Dear Madam/Sir,
>
> I have to construct a dynamic building-metro and there are three input
> temperatures (soil temperature, tunnel temperature and ambient
> temperature) but only one Type 56 can be used in the model (only one
> input temperature). How can I set three input temperatures in the
> building model?
>
> --
> Best Regards
> Qi Cheng
>
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20131121/97b675f3/attachment-0001.htm>
More information about the TRNSYS-users
mailing list