[TRNSYS-users] Type 60c outlet temperature
David BRADLEY
d.bradley at tess-inc.com
Tue Apr 8 10:34:04 PDT 2014
Barto,
It is not really possible to diagnose the problem without looking at
the project. I would recommend using an online plotter to look at all of
the temperatures and flow rates of all the flows going into and coming
out of the tank. If for some reason all of the temperatures in the
system are over 60C (including the temperature of the tempering water)
then Type953 would not be able to temper the outlet flow. It could also
be that you are seeing higher than 60C temperature at the mixing valve
when there is no flow through the valve.
If you are not able to sort out the problem using Type65 as a
debugging tool then you should send your project to your distributor so
that they can have a look at it.
Kind regards,
David
On 4/7/2014 08:16, Barto Pene wrote:
> Hi ,
>
> I get some strange result i.e I can not find logic in it: I use tank
> Type 60c only heated by standard solar collector installation. I use
> the differential controller(monitoring temp.) to limit the tank top
> temperature to 60C and I'm also using tempering valve Type 953 with
> diverting and three-wat valves for controling the outlet temp. In the
> simulation I get temperatures at the outlet of the three-way valve
> (after mixing) higher than 60C (even 80-90C) how is it possible?
>
> When I model the HX in Type60c with glycol solution I get convergence
> problems and with water there is no problem...?
>
> Thank you
>
> Regards
> Barto
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at cae.wisc.edu
> https://mailman.cae.wisc.edu/listinfo/trnsys-users
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140408/be4edc82/attachment-0001.htm>
More information about the TRNSYS-users
mailing list