[TRNSYS-users] Thermal mass is not considered in Type	56	simulation!!
    marcello.caciolo at cofelyaxima-gdfsuez.com 
    marcello.caciolo at cofelyaxima-gdfsuez.com
       
    Wed Jul 23 23:50:22 PDT 2014
    
    
  
Dear Mehrdad,
I do not know what you expected, but the graph you show is correct : internal temperature changes are slower in the heavy building. Try to put some intermittent internal gains and you will amplify this effect.
Best regards,
Marcello Caciolo
Responsable Outils et Méthodes d'Analyse Energétique
[cid:image001.jpg at 01CFA71C.4DF99980]
Cellule Efficacité Energétique et Environnementale - Pôle Projets et Réalisations
46 Boulevard de la Prairie au Duc
BP 40119 - 44201 Nantes Cedex 02
Tél.: +33 02 40 41 06 57
marcello.caciolo at cofelyaxima-gdfsuez.com<mailto:prenom.nom at aximaseitha-gdfsuez.com>
P Pensez à l'environnement avant d'imprimer ce message
De : TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org] De la part de Mehrdad Farshchi
Envoyé : jeudi 24 juillet 2014 07:06
À : TRNSYS users mailing list at OneBuilding.org; jlam at transsolar.com
Objet : Re: [TRNSYS-users] Thermal mass is not considered in Type 56 simulation!!
Dear Jochen,
Thank you for your email. I have modelled and simulated a simple rectangular building (15m x10m) in Sydney with Trnsys 17 software. Then using the Trnsys library I have edited the building components in order to make a heavy weight building as follows:
Floor = BST_H_FLO                   (see the figure attached)
External Wall = BST_H_EXT   (see the figure attached)
Roof= BST_H_ROO                  (see the figure attached)
Although Infiltration, Ventilation, Heating, Cooling and Comfort regime are off, the observed thermal lag was very low (less than an hour). Even I changed the wall concrete thickness to 0.4m and the result for the air temperature (TAir_H_0.4) did not show any changes in terms of thermal lag (please have a look at the graph attached)
Tambient: ambient temperature ,
TAIR_H_0.1:  air temperature of air node with above mentioned building component and setting and
TAIR_H_0.4 : air temperature of air node with above mentioned building component and setting the wall concrete thickness to 0.4m.
I wonder if you could please let me know how to resolve this issue.
Kind Regards
Mehrdad
On Thu, Jul 17, 2014 at 6:40 PM, hotline <hotline at transsolar.com<mailto:hotline at transsolar.com>> wrote:
Dear Mehrdad,
TYPE 56 considers thermal masses. I can imagine that you’ve set a high ventilation rates.
If so, you might compare the surface temperatures or the operative temperature instead.
Best
__________________________________________________________________________________________________
Jochen Lam
TRNSYS Software Team
Transsolar Energietechnik GmbH
Curiestraße 2
70563 Stuttgart
Fax:        +49 711 67976-11<tel:%2B49%20711%2067976-11>
Email:    jlam at transsolar.com<mailto:jlam at transsolar.com>
Web:      www.trnsys.de<http://www.trnsys.de/>
Von: TRNSYS-users [mailto:trnsys-users-bounces at lists.onebuilding.org<mailto:trnsys-users-bounces at lists.onebuilding.org>] Im Auftrag von Mehrdad Farshchimonfared
Gesendet: Mittwoch, 16. Juli 2014 06:12
An: trnsys-users at cae.wisc.edu<mailto:trnsys-users at cae.wisc.edu>
Betreff: [TRNSYS-users] Thermal mass is not considered in Type 56 simulation!!
Dear Trnsys users,
I have modelled a residential building with different building components (including different thermal masses) using Trnsys 3d, Type 56 . The simulation results show no thermal lag between hourly inside air temperature of each zone even if, the heavy materials are used. It is weird as it seems that Trnsys does not take into account the thermal mass of walls, floors and etc.
Have you come across with this problem previously?
If  yes, I wonder if you could please let me know how to resolve this issue as soon as possible.
Kind Regards
Mehrdad
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at lists.onebuilding.org<mailto:TRNSYS-users at lists.onebuilding.org>
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140724/bb551c46/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 4267 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140724/bb551c46/attachment-0002.jpg>
    
    
More information about the TRNSYS-users
mailing list