[TRNSYS-users] Trnsys Project
David BRADLEY
d.bradley at tess-inc.com
Thu Sep 4 09:46:16 PDT 2014
Eleonora,
Your Type56 building is in Energy Rate Control meaning that you are
predefining a zone temperature and allowing the model to compute the
energy required to maintain that temperature (the load). When you want
to simulate a system, you need to move from Energy Rate Control to
Temperature Level Control where you allow the zone temperature to float,
you define a thermostat and the equipment that will deliver energy to
the space (a fan coil or a radiator). The thermostat will watch the zone
temperature and turn on and off the equipment in an attempt to maintain
the desired set point. There is a tutorial called "Temperature Level
Control from Energy Rate Control" available at:
http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm
It will step you through the process that you can then apply to your
building and system.
Regards,
David
On 9/3/2014 13:13, ELEONORA SANESI wrote:
> Hi I'm Eleonora and I study environmental engineering.
> For my thesis next month I have to model a real simply building but I
> have a problem.
> My building have the solar thermal collectors link to the boiler link
> to a pump.
> My problems is how to link this sistem to my type56.
> I send you my project in the hope of your answer.
> Thanks a lot
> Eleonora Sanesi
>
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley at tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20140904/3ee8db81/attachment-0002.htm>
More information about the TRNSYS-users
mailing list